I would only remove CPCs while testing new circuits I've installed. If the installation isn't mine far safer to leave CPCs installed.
And know as long as Ze is good all others circuits should be safe.
 
Really? Never been taught that, why is that then wouldnt it provide voltage onto other CCT's?

See 612.3.1 of the current regs: The insulation resistance shall be measured between live conductors and between live conductors and the protective conductor connected to the earthing arrangement.

If the line and neutral are disconnected, there's no reason that any test voltage would affect other circuits. However I would avoid IR testing with other local circuits energised.
 
Wow thanks, well I have learned something today. P.S. I did actually look at it, mustnt just follow OSG then.(note to self)
That requirement came in with the 17th Edition in 2008. Without the earthing arrangement being in place and the cpc connected to the MET then you may have a fault between live conductors and earth but not to the cpc of the circuit.
 

Reply to How would you advise customer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
563
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
937

Similar threads

Another tip for metal boxes, the single box version…. Is to fold flat the fixing lugs that you won’t be using… the top and bottom ones
Replies
9
Views
530
Depending on the location of the 2 CU's and the quality of materials I'd say £10K-12K. If they're potential tyre kickers don't waste loads of time...
    • Informative
Replies
4
Views
342

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top