Well I just removed the whole lighting cable and tested IR from CU end so LNE were disconnectedWhy are you disconnecting cpc in cu for IR
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss How would you advise customer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Well I just removed the whole lighting cable and tested IR from CU end so LNE were disconnectedWhy are you disconnecting cpc in cu for IR
Well I just removed the whole lighting cable and tested IR from CU end so LNE were disconnected
Really? Never been taught that, why is that then wouldnt it provide voltage onto other CCT's?Cpc should remain in MET during IR testing
Yes but dont forget I was only checking the lighting circuit in particular and the other circuits were on.I would only remove CPCs
Really? Never been taught that, why is that then wouldnt it provide voltage onto other CCT's?
Wow thanks, well I have learned something today. P.S. I did actually look at it, mustnt just follow OSG then.(note to self)connected to the earthing arrangement
That requirement came in with the 17th Edition in 2008. Without the earthing arrangement being in place and the cpc connected to the MET then you may have a fault between live conductors and earth but not to the cpc of the circuit.Wow thanks, well I have learned something today. P.S. I did actually look at it, mustnt just follow OSG then.(note to self)
Not usually I start with testing all together and only break it down if there is a low IR, as I say I needed to separate this circuit in particular. It was a one off really.connected to the earthing arrangement.