Just wondering how you guys think about this.
It’s a minefield.

[ElectriciansForums.net] How’s this gonna work...overloading
 
Last edited:
Just fit populated rcbo boards,would that work?
My take is yes, that's fine. They don't like the RCD with say 80A rating sitting between the suppliers 100A fuse and a row of MCB that add up to more than 80A. They are saying (don't know if true) that we are no longer allowed to use diversity as per OSG.
 
Design current is as always the determining factor. You could theoretically have a row of 99 x 32A MCBs all protecting circuits not pulling more than 1A and your 100A main switch would be absolutely fine.

This is just Hager up to its usual tricks.

Scare
Scare
Scare
Scare
Scare
Scare
Scare
Buy more of our RCBOs
Scare
Scare
Scare
Etc...
 
Design current is as always the determining factor. You could theoretically have a row of 99 x 32A MCBs all protecting circuits not pulling more than 1A and your 100A main switch would be absolutely fine.

This is just Hager up to its usual tricks.

Scare
Scare
Scare
Scare
Scare
Scare
Scare
Buy more of our RCBOs
Scare
Scare
Scare
Etc...

Yup .......... that pretty much sums it up

AND this is why manufacturers should NOT be allowed anywhere near JPEL/64 or ANY of its sub committees

Talk about vested interests


BUT they could "fix" the problem by fitting 100A RCD's in their dual boards........
 
Thanks @westward10 for finding the source in 7671.

I think 536.4.202 may be helpful here. The last paragraph (which H appear to have used only in part) also says that things "shall be selected in accord with manufacturer's instructions". So if a Wylex board is rated at 100A and sold equipped with two 80A RCD we should be able to rely on them to have got that part right (?). We then keep the connected load after diversity to less than 80A as per usual.
 
My take is yes, that's fine. They don't like the RCD with say 80A rating sitting between the suppliers 100A fuse and a row of MCB that add up to more than 80A. They are saying (don't know if true) that we are no longer allowed to use diversity as per OSG.

Completely pointless fitting RCBOs if your main switch is rated at 60A and the combined total load and OCPD for the CU is above that.
 

Reply to How’s this gonna work...overloading in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Persons who are not registered with a self-certification scheme - including DIYers - will need to notify or submit plans to a Building Control...
Replies
1
Views
412
  • Question
day rate or hourly....I prefer hourly and then it stops them moaning if you are ten mins late one day
Replies
3
Views
606

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top