Found this on my travels today visiting my favourite customers. I hadn't noticed this previously and I can only assume this is the result of a recent 'solar PV service' the customer had last month.

My customer asked for my opinion as she had also not noticed the wire previously, the words 'I dunno, but summat smells fishy' were in my head and on the tip of my tongue but the what came out was "F*ck, that looks ropey as!".

I assume this isn't standard practice to wedge a wire in with a fancy twist to get the 3 phase solar PV to trip. Should the correct item should be a 3 Phase 16A MCB rather than 3 tied together?

[ElectriciansForums.net] I always wondered what the little holes are for!
 
The discussion on mcb and rcbos is about what’s beside the 3x SPMCB’s linked together as to why they both look different.

From this quoted posted.

Just was comparing it with the S.P. ones in the D.B. but I suppose they are an older version.

And I said I think they’re rcbos.
 
Thanks for replies chaps.

If you hadn't of guessed already, I know naff all about PV. Could anyone explain what this workaround is trying to achieve?

What would happen if the link isn't in and a single phase drops off? Would the invertor be damaged or just a lack of balanced power back to the grid/less generated power being fed back/less income?
 
Nice attempt to dodge the bullet of being wrong! Why point out what the other PDs are when the op is referring to the MCBs? I’m very confused
Not dodging anything, as you say your a little confused.
Anthony brag was compairing them with the other single pole devices in post 5.
But Phil Thompson correctly pointed out they where RCBO,s in post 6. I agreed with Phil Thompson.
 
Come on guys and girls, that's a big no no mod. Expected one MCB trip to switch all three is asking a bit much. What if one trys to trip, and the other two mcb's says no your not. I think you can see what could happen next. The big and only answer to thist is get this/who firm to court.
 
Come on guys and girls, that's a big no no mod. Expected one MCB trip to switch all three is asking a bit much. What if one trys to trip, and the other two mcb's says no your not. I think you can see what could happen next. The big and only answer to thist is get this/who firm to court.

I think we already agree on that one.
 
Some 1 pole MCBs can be linked together, I've seen it in control circuits on multi-phase or multiple supplies (essential & non-essential etc) ...but it is achieved using a linking mechanism that connects adjacent MCBs through a removable cover on the side of the MCB.
HOWEVER these link kits usually include a link bar.

So I agree with the consensus that a piece of copper wire used as a link bar is definitely dodgy.
 
Really!!
which ever way you spin this it has a bad feel to it.
Whats the rest of the PV instal like?
DC string or microinverters??
I'd want to cast a very critical eye over the whole PV system.
If it's a DC string system just remember it will be generating high voltage DC not a huge current but if a fault develops in the DC side it can have very nasty consequences
 
Thanks for the comments, I don't think the install is particularly good to be honest.

I do not know any details of the installation company and whether the main electrical contractor also installed the PV or not but there are a lot of other very curious installation 'quirks' that I do not think are correct.

The more I look the worse it gets, I have just been fire fighting at the moment doing the critical work. I shall be back in the new year to carry out a full report and tidy the DB. Who knows what lurks inside there but I know rats would be right at home in there!

edit: I guess it would be the last one to touch the board would be in court defending himself (me) and the PV guy should be sweating!
 
Hm. Given the feed in tariff is about to vanish I wouldn't be surprised if a lot of questionable companies are throwing out as many installs as they can to clear stock and get their cheques from the government before they quietly dissolve the company and swan off to pastures new!
 

Reply to I always wondered what the little holes are for! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top