banny07

-
Arms
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I test zs it 8.26 ohm new to testing. I even buypassed rcbo but it stays same. Do you think my mft if faulty? Any thoughts guys? I am new to testing.
 
Last edited:
I didn't know that. I thought zs db/circuit should be tested with all parallel path connected.
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
 
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
so at the furthest point with all the parallel earth paths removed
by disconnecing main bonding conductors to water and Gas?
 
I didn't know that. I thought zs db/circuit should be tested with all parallel path connected.
That's actually how I was taught and what GN3 appears to say; Julie's logic and reasoning is spot on, and in this case I might have done it anyway to help build a picture of what is going on.
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
No argument about the logic/reasoning. I'm also mindful that GN3 implies that in all circumstances where you have live final circuits (required for these tests) you should have the bonding connected. But it also doesn't specifically describe the Zdb test as far as I can tell.

It only seems to discuss two cases - testing external earth loop impedance with main earth disconnected, and all other earth loop impedance tests where it says that "for safety and practical reasons neither the connection with Earth nor bonding conductors are disconnected". (Page 66)
So while I think it might have been a handy test to do I wouldn't say the OP is doing it wrong either.
 
That's actually how I was taught and what GN3 appears to say; Julie's logic and reasoning is spot on, and in this case I might have done it anyway to help build a picture of what is going on.

No argument about the logic/reasoning. I'm also mindful that GN3 implies that in all circumstances where you have live final circuits (required for these tests) you should have the bonding connected. But it also doesn't specifically describe the Zdb test as far as I can tell.

It only seems to discuss two cases - testing external earth loop impedance with main earth disconnected, and all other earth loop impedance tests where it says that "for safety and practical reasons neither the connection with Earth nor bonding conductors are disconnected". (Page 66)
So while I think it might have been a handy test to do I wouldn't say the OP is doing it wrong either.
That's really why measuring R1+R2 dead, and calculating zs from the ze/zdb + the measured circuit loop resistance is the usual practice, it allows you to obtain the minimum zs whilst not exposing users to an un-bonded system.
 
by disconnecting main bonding conductors to water and Gas?
Exactly.

Just as @Julie. says when you have the bonding in place you might have parallel paths lowering the supply's R2, hence you might see a much higher PFC and that is something to take in to account when verifying that OCPD is able to safely interrupt it.

However, such parallel paths are not guaranteed to remain. So if someone replaces some of a metal water pipe with plastic you might lose a parallel path and so the only safe assumption is the supply earth is there for faults. So checking Ze allows you to check that under a change of bonded part(s) you are still able to disconnect fast enough under fault conditions.
 
Yes, typically the only way to measure Ze is to isolate the installation supply (usually via the incoming switch) so it is completely dead, and then disconnect the supply earth and measure to it, and put it back immediately. Removing the bond conductors might do it, but as you can have links from the installation CPC to extraneous metalwork via boiler CPC, immersion heater CPC, or supplementary bonding, etc, you can never be sure.

Measuring Zs is simpler as everything is still in place. Of course if the supply earth is faulty then you would risk raising the CPC and any extraneous parts with a high impedance to potentially dangerous voltages, but most MFT will usually throttle the test current if they see a voltage change that could exceed 50V to keep things reasonably safe.
 

Reply to the thread, titled "I am getting very high zs readings" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

banny07

Arms
-
Joined

Thread Information

Title
I am getting very high zs readings
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
banny07,
Last reply from
Inteificio,
Replies
27
Views
9,495

Advert

Back
Top