banny07

-
Arms
Joined
Aug 2, 2009
Messages
193
Reaction score
39
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I test zs it 8.26 ohm new to testing. I even buypassed rcbo but it stays same. Do you think my mft if faulty? Any thoughts guys? I am new to testing.
 
Last edited:
I didn't know that. I thought zs db/circuit should be tested with all parallel path connected.
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
 
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
so at the furthest point with all the parallel earth paths removed
by disconnecing main bonding conductors to water and Gas?
 
I didn't know that. I thought zs db/circuit should be tested with all parallel path connected.
That's actually how I was taught and what GN3 appears to say; Julie's logic and reasoning is spot on, and in this case I might have done it anyway to help build a picture of what is going on.
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
No argument about the logic/reasoning. I'm also mindful that GN3 implies that in all circumstances where you have live final circuits (required for these tests) you should have the bonding connected. But it also doesn't specifically describe the Zdb test as far as I can tell.

It only seems to discuss two cases - testing external earth loop impedance with main earth disconnected, and all other earth loop impedance tests where it says that "for safety and practical reasons neither the connection with Earth nor bonding conductors are disconnected". (Page 66)
So while I think it might have been a handy test to do I wouldn't say the OP is doing it wrong either.
 
That's actually how I was taught and what GN3 appears to say; Julie's logic and reasoning is spot on, and in this case I might have done it anyway to help build a picture of what is going on.

No argument about the logic/reasoning. I'm also mindful that GN3 implies that in all circumstances where you have live final circuits (required for these tests) you should have the bonding connected. But it also doesn't specifically describe the Zdb test as far as I can tell.

It only seems to discuss two cases - testing external earth loop impedance with main earth disconnected, and all other earth loop impedance tests where it says that "for safety and practical reasons neither the connection with Earth nor bonding conductors are disconnected". (Page 66)
So while I think it might have been a handy test to do I wouldn't say the OP is doing it wrong either.
That's really why measuring R1+R2 dead, and calculating zs from the ze/zdb + the measured circuit loop resistance is the usual practice, it allows you to obtain the minimum zs whilst not exposing users to an un-bonded system.
 
by disconnecting main bonding conductors to water and Gas?
Exactly.

Just as @Julie. says when you have the bonding in place you might have parallel paths lowering the supply's R2, hence you might see a much higher PFC and that is something to take in to account when verifying that OCPD is able to safely interrupt it.

However, such parallel paths are not guaranteed to remain. So if someone replaces some of a metal water pipe with plastic you might lose a parallel path and so the only safe assumption is the supply earth is there for faults. So checking Ze allows you to check that under a change of bonded part(s) you are still able to disconnect fast enough under fault conditions.
 
Yes, typically the only way to measure Ze is to isolate the installation supply (usually via the incoming switch) so it is completely dead, and then disconnect the supply earth and measure to it, and put it back immediately. Removing the bond conductors might do it, but as you can have links from the installation CPC to extraneous metalwork via boiler CPC, immersion heater CPC, or supplementary bonding, etc, you can never be sure.

Measuring Zs is simpler as everything is still in place. Of course if the supply earth is faulty then you would risk raising the CPC and any extraneous parts with a high impedance to potentially dangerous voltages, but most MFT will usually throttle the test current if they see a voltage change that could exceed 50V to keep things reasonably safe.
 

Reply to I am getting very high zs readings in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
749
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
939

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top