Piratepete

Hoping to get sensible suggestions for this.

Family in semi-detached house are getting 'tingles' from the basin taps in their bathroom. They're the sensible sort so I have no reason to doubt them. Hubby is technical. He says they've only noticed it recently. But it also happens with the consumer unit turned off!

I've been in and could find nothing wrong. Did bonding tests on pipework and the bath (metal), insulation tests at the CU. All seems fine. Western Power guys had a look, changed the cutout (old one probably 60 years old). The floor is lino (very high IR to earth)

This is an extract of their latest email about the problem.

>'Update on the bathroom problem:

With regard to the odd bathroom problem; it still happens, intermittently, and is definitely apparent when in the bath - despite your measurements showing decent continuity between the two. I can’t explain it, but it is definitely not in my head!! Via a cheapo multimeter I think I’ve ascertained the following...


  • It measures about 1.5V AC between bath water or wet floor and taps/radiator
  • If measured on DC setting, it shows about 0.8V with positive polarity on the water end
  • It is present even if our consumer unit is isolated from the supply
  • The duty cycle setting on the meter shows 50Hz
Could it be something dodgy in the neighbouring property, coming through the ground/drainage? I don’t understand it and can’t explain it - but it’s there. Sometimes.
Is it worth adding some additional bonding between the bath an the pipework, or at least retesting the impedance between the two? I don’t want to worry about nothing, but with a small child and pregnant wife it’s bugging me still.'<

So guys, what should I do next. Nothing rude please!
 
OP Here.
Tingley Taps link very interesting. Details of my problem below.
House is a 30s semi in a village street. Supply is underground TN-S, new (yesterday) 100 amp cutout.
Zs at CU 0.16, PFC 1.45 kA, Earthing in 16mm, Bonding 10mm. CU 16th Ed.
IR All circuits L+N/E 1.44 MOhm.( It's the downstairs ring cct bringing it down but boiler has no proper isolator (unswitched FCU) and couldn't disconnect the fridges). But it passes and is not relevant!

With CU off, current through main earth is 0.4mA DC, 2.6mA AC
With CU on, current through main earth is 0.4mA DC, 5.0mA AC

The bath taps are effectively (measured) well bonded but between the metal plughole and the taps the resistance is 960 Ohms. The voltage between the plughole and the taps is 0.47 VDC and 0.51 VAC. Ohms law gives you 0.48 mA DC which ties up nicely with the current I measured on the main earth.
The client's testmeter (which cost a bit more than £5) gives the same readings.
He says that the voltage rises to 1.5 VAC and 0.8 VDC when they get the tingles (with the CU off).

Can't see under the bath due to the side panel being (permanent) but the bath waste coming through the wall is in lead, no doubt all the way to the trap!

I'll be having a word with Western Power Distribution in the morning!

Cheers
Pete

Is this bath an iron bath??
 
Yes. I'm hoping the side panel will be deconstructd by the morning!


If the pipes supplying the bath taps are copper it could be worth chopping a lump out of both the hot & cold ( say about 8 inches) and sticking a bit of plastic in its place (Speedfit for example)

Same goes for the basin.

If the bath is iron, then consider replacing he lead waste with 40mm plastic.

These measures are not intended to be a substitute to finding and fixing the fault it's more like an extra line of defence if you like.
 
Hi the problem at the hall toilets was:

the earth system was TNS so at the origin of supply you have an earth point at X amount of ohms
you have water & maybe gas bonding connected to this point bringing them to the same potential or close to it.
Then you have maybe your bath waste being metal at a different point could be 10-20 meters away could even be next to the cut out this if metal is going into the ground creating another point to earth at say XX.
When the water is run in the bath or in our cAse was the sink & you touched the taps whilst your hand was in the water you would get the tingling sensation our case was because we got around 65v difference, I believe touch voltage 50v am I correct not sure, now under Dry conditions you would not as likely feel this but when your hands ect are wet you are feeling it. (& touch voltage value is halved)
This is because the earth points are at different potential points as it would be in the above as the mass of the earth at the two different points is different.
also before our problem occurred we had just installed cross bonding to all hot & cold pipe work but could not see the metal waste when cross bonded with others what happened ... They were at the same potential or close to it so no more problem.
What made more Intresting was during testing we found neutral outside was breaking down at the pole joint & we had just had it repaired also.

With regard to chopping out a bit of pipe on the hot &'cold water pipes at the bath, what do you think this will do as water is conductive & unless they are running a sand bath there is nothing this will do. Now if you replaced the bath wate with plastic & into hopper or plastic soil stack that would work why bother though when the simple thing would be to bring them to the same potential by ? Cross bonding them together.
 
Last edited:
How can it measure AC and DC current seperately in the same conductor? I think you will find it is measuring AC current on both ranges but is giving a false reading on the DC range as it is trying to make sense of an AC!
That looks like multimeter according to google, did you disconnect the earthing conductor and inset this meter in to it? Or do you have a clamp type adaptor for it?

Of course the suppliers earth isn't at the earth potential of the local ground, did you expect it to be?

Well. I thought of that and tested my meter when I got home on known 12VDC and 230VAC supplies. On that limited test the DC setting doesn't recognise the AC and vice versa. Also the DC at the bath is polarity sensitive.

I accept that the suppliers earth isn't at earth potential. But would you expect this current to flow through it? Presumably, if I bond the waste, the current will increase (960 Ohms removed).

Pete
 
Hi the problem at the hall toilets was:

the earth system was TNS so at the origin of supply you have an earth point at X amount of ohms
you have water & maybe gas bonding connected to this point bringing them to the same potential or close to it.
Then you have maybe your bath waste being metal at a different point could be 10-20 meters away could even be next to the cut out this if metal is going into the ground creating another point to earth at say XX.
When the water is run in the bath or in our cAse was the sink & you touched the taps whilst your hand was in the water you would get the tingling sensation our case was because we got around 65v difference, I believe touch voltage 50v am I correct not sure, now under Dry conditions you would not as likely feel this but when your hands ect are wet you are feeling it. (& touch voltage value is halved)
This is because the earth points are at different potential points as it would be in the above as the mass of the earth at the two different points is different.
also before our problem occurred we had just installed cross bonding to all hot & cold pipe work but could not see the metal waste when cross bonded with others what happened ... They were at the same potential or close to it so no more problem.
What made more Intresting was during testing we found neutral outside was breaking down at the pole joint & we had just had it repaired also.

With regard to chopping out a bit of pipe on the hot &'cold water pipes at the bath, what do you think this will do as water is conductive & unless they are running a sand bath there is nothing this will do. Now if you replaced the bath wate with plastic & into hopper or plastic soil stack that would work why bother though when the simple thing would be to bring them to the same potential by ? Cross bonding them together.


Clean,potable water is not as conductive as you may imagine.

You can actually make a rudimentary speed control rheostat,using the varying proximity of two copper wires,in a bowl of water!

...Just adding a bit of fun :joker:

NB; Also,do not discount a possible fault occurring,in an adjacent property,where your shared soil may be receiving an unwanted input from their supply...
 
Last edited:
Your joking, I used off cuts of 2x½” tinned copper busbar about 15” long. Lead, tin and copper would make it your last cup of tea.

I’d read about electrode boilers and as I was bored one Sunday afternoon at work I decided to have a play. It was only a square plastic bowl with the sections of busbar along opposite sides, 250V between them. The power can be regulated by altering the distance between the bars. I got it up to about 12KW 45A before blowing the 32A fuse. It gets downright violent once the temperature is getting close to boiling point. The workshop was like a sauna.

On a Sunday all the plants would be running flat out, if nothing broke down I’d got time to kill. I found something to keep me entertained for a while.

This is not an experiment to try at home! A/ it’s dangerous, B/ you’ll have to pay the lecy bill!
 
Hi the problem at the hall toilets was:

the earth system was TNS so at the origin of supply you have an earth point at X amount of ohms
you have water & maybe gas bonding connected to this point bringing them to the same potential or close to it.
Then you have maybe your bath waste being metal at a different point could be 10-20 meters away could even be next to the cut out this if metal is going into the ground creating another point to earth at say XX.
When the water is run in the bath or in our cAse was the sink & you touched the taps whilst your hand was in the water you would get the tingling sensation our case was because we got around 65v difference, I believe touch voltage 50v am I correct not sure, now under Dry conditions you would not as likely feel this but when your hands ect are wet you are feeling it. (& touch voltage value is halved)
This is because the earth points are at different potential points as it would be in the above as the mass of the earth at the two different points is different.
also before our problem occurred we had just installed cross bonding to all hot & cold pipe work but could not see the metal waste when cross bonded with others what happened ... They were at the same potential or close to it so no more problem.
What made more Intresting was during testing we found neutral outside was breaking down at the pole joint & we had just had it repaired also.

With regard to chopping out a bit of pipe on the hot &'cold water pipes at the bath, what do you think this will do as water is conductive & unless they are running a sand bath there is nothing this will do. Now if you replaced the bath wate with plastic & into hopper or plastic soil stack that would work why bother though when the simple thing would be to bring them to the same potential by ? Cross bonding them together.

Are you sure about that??

Try a little experiment sometime with two bits of copper pipe joined together by a bit of plastic pipe about a foot long, fill with water and stick your meter on it.
 
so we have a bath with say some water in it, you have metall tap that is bonded has water in pipe upto outlet running or not, maybe wet hands so you are touching the taps with wet hands & splashing around a little then you could get a shock From the PD, as mentioned we had similar problem on a sink at a hall after cross bonding. I did not think it could happen & even touched both parts but was when my hands were wet did I get the tingly feeling & then see the voltage.
I am sure that I would cross bond it rather than chop out a bit of copper to install a bit of plastic & are you sure I am not correct without putting it to the test I would not know Would you then?
I know I would not take the risk & go for the cross bond on a PD like that
 

Reply to I do seem to getem! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
831
J
  • Article
Have my water pipes been plumbed the wrong way? Good morning, I recently had an extension, new bathroom and new en-suite fitted. Prior to the...
Replies
0
Views
216
jennys07
J
  • Article
This is an RSS feed of thread: Why do I have no hot water? Please help Content of the thread: Hi About 8 years ago the valve under the sink...
Replies
0
Views
216
  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
Replies
15
Views
2K
M
  • Article
Intermittent bad smell Hi I have an intermittent bad smell that's really hard to pin down, I was wondering if I could get your thoughts on it...
Replies
0
Views
185
MatthewG
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks