Hello guys and girls,

I have two questions, the first one is......

when testing insulation resistance if you were to double the cable the insulation resistance would half ?
something about parallels ? what does this mean ?

Second question is.....

the relationship between the maximum PFC and the breaking capacity of a protective device is supposed to be that the protective device is greater than than the measured PFC ? is that correct ?

i thought the breaking capacity of the breaking device had to be lower than the measured PFC ?
 
The resistance of a conductor is directly proportional to its length (L) as R ∝ L. Thus doubling its length will double its resistance, while halving its length would halve its resistance. Also the resistance of a conductor is inversely proportional to its cross-sectional area (A) as R ∝ 1/A

This article on Professional Electrician.com may answer your other query re: RCD breaking current relationship with PFC
Code:
/technical/prospective-fault-current/

The experts at NICEIC provide us with more critical best practice advice.
Either by enquiry, measurement or calculation, prospective fault current (Ipf) should be determined at every relevant point within an installation (Regulation 434.1). The values obtained should be compared against the relevant installation design criteria to confirm that the fault rating of each device is not less than the maximum prospective fault current that may occur at that particular point in the installation (Regulation 434.5.1).

For many smaller installations, especially domestic installations, verification is normally a matter of confirming that all installed protective devices have a greater rated braking capacity than the maximum value of prospective fault current determined for the installation.

The maximum value is the higher of the maximum prospective short-circuit fault current (line-to-neutral) and the maximum prospective earth fault current (live to earth), and must be recorded in the relevant section of an NICIEC electrical certificate or report.

Where the maximum prospective fault current is determined by testing, the ‘live’ test should be performed at the origin of the installation where the fault current is highest, such as at the distribution board or consumer unit or other switchgear supplied directly from the distributor’s equipment.

With the main switch ‘OFF’ the short circuit test is performed as shown in Fig 1. An earth fault current test should also be made and the higher of the readings taken should be recorded as the maximum value of prospective fault current.

The earthing conductor, main protective bonding conductors and circuit protective conductors should all be connected during these tests, because the presence of these and any other parallel paths to Earth may reduce the impedance of the fault loop and so increase the prospective fault current.

Conditional rating


Where a consumer unit to BS EN 61439-3 is installed in domestic or similar premises, the arrangement of the devices and the outer enclosure (of the consumer unit) is designed to safely withstand a prospective fault current of up to 16 kA.

In such circumstances, the maximum prospective fault current should be recorded as 16 kA in the relevant part of the electrical certificate or report, and undertaking prospective fault current testing at any point in the installation would be considered unnecessary.

In some cases, prospective fault current testing may need to be carried out at other relevant points in the installation, particularly at the furthest points, to confirm that the fault current is sufficient to cause operation of the protective device before the permitted limiting temperature of any conductor or cable is exceeded (Regulation 434.5.2).

The relationship between the protective device and the cable

For any relevant disconnection time the maximum energy withstand of the cable must be greater than the let- through energy of the protective device. If this is not the case, there is the risk that under fault conditions the conductor or cable may suffer thermal damage and as a result it may have to be replaced. This thermal relationship can be stated as:

S2 k2 ≥ I2t

To illustrate this relationship, Fig 2 shows a 16 mm2 cable incorporating an uninsulated 6mm2 protective conductor supplying a load. The circuit has been installed using a 70 °C thermoplastic insulated and sheathed flat cable (copper) and is protected by a BS 88-3 type (C) fuse, rated at 63 A. (Assuming a TN earthing system for the installation, a disconnection time of 5 s is permitted by Regulation 411.3.2.3 of BS 7671).

The maximum thermal withstand of the cable depends on its cross-sectional area S and also K which is a factor that takes account of the material properties of conductors and insulation.

From Table 54.3 of BS 7671 the value of k for the cable shown in Fig 2 is 115, and so, the maximum thermal withstand of the cable can be calculated as follows:

Code:
Maximum thermal cable withstand = S2 k2 = (6² x 115²) = 476 100 J

As shown by the calculations in Fig 2, the cable is exposed to a higher fault current at position (A) than at position (B). However, a fault occurring at position (B) represents the most onerous condition because the lower fault current leads to a longer disconnection time, which results in a higher let-through energy I2t.

Table 1 is based on Appendix 3 (Fig 3A1) of BS 7671, and shows the time/current disconnection values for a BS 88-3 fuse rated at 63 A, from which the respective let-through energy I²t has been calculated.

As the required disconnection time increases from 0.1 s to 5 s, the minimum current required to disconnect the 63 A fuse decreases (inverse characteristic of the fuse). For a fault of 320 A (position B) the energy let-through of the protective device exceeds 476 100 J, the maximum thermal withstand of the cable.

It should be noted that only the earth fault current is determined in the example because the protective conductor is of a reduced cross-section so it will have a higher resistance and therefore a lower prospective fault than that resulting from a short-circuit. However, where necessary the short-circuit fault current should also be determined.

[ElectriciansForums.net] I HAVE TWO QUESTIONS[ElectriciansForums.net] I HAVE TWO QUESTIONS
 

Attachments

  • Resistivity Handout.docx
    278.5 KB · Views: 1
Last edited:
Lister 1987: What you wrote about resistance is true but does not address the OP's question. Grab a tea and re-read what the OP asked. What you know about resistance should then help you answer. Draw a diagram which shows all the resistances to help you define the question. :)
 
the relationship between the maximum PFC and the breaking capacity of a protective device is supposed to be that the protective device is greater than than the measured PFC ? is that correct ?

i thought the breaking capacity of the breaking device had to be lower than the measured PFC ?

The PFC you measure tells you the maximum current which could flow in a worst case fault situation.
The breaking capacity of the device tells you the maximum current which it can safely break, anything above this and the device may weld closed or otherwise not break the fault.

So for a protective device to be able to protect an installation it needs to be have a breaking capacity higher than or equal to the prospective fault current.
 

Reply to I HAVE TWO QUESTIONS in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top