Hi Ron,

When testing the RFC R1+R2 cross connected at the CU, and then going round all the sockets, this should have highlighted the problem.

An IR test would not pick this up as there was a break in the circuit, which to be honest, probably made the readings quite good!

It highlighted the problem but only in the same way as the end to end continuity test. It did not help find the break because RI+R2 cross connected at the meter with a break in R2 gives open circuit at every socket on the ring. Linking the 2 N's & 1 cpc (or 2 L's & 1 CPC) was the only way I could think to find the break.

You hit the nail on the head though regarding the IR test and on the basis it was good I went ahead but in future it will make me think.

Cheers, Ron
 
It highlighted the problem but only in the same way as the end to end continuity test. It did not help find the break because RI+R2 cross connected at the meter with a break in R2 gives open circuit at every socket on the ring. Linking the 2 N's & 1 cpc (or 2 L's & 1 CPC) was the only way I could think to find the break.

You hit the nail on the head though regarding the IR test and on the basis it was good I went ahead but in future it will make me think.

Cheers, Ron

Yes good point.

This does go to show however, that any testing is not always conclusive.

At least you found the fault.:)
 
IEE guidance note 3 section 2.7.4 The sequence of tests, sets out the corect order in which tests should be performed.

Regards

Quite correct and the first on the ring is the end to end continuity.

But also think carefully about the tests and not one of them would help pinpoint this fault, they would only show a fault i.e open circuit. You have to think about ways to locate it and they are not in the book.

Cheers, Ron
 

Reply to I.R test before cu changeI in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
221
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
836
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
830

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
481
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
489

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top