Hi Ron,

When testing the RFC R1+R2 cross connected at the CU, and then going round all the sockets, this should have highlighted the problem.

An IR test would not pick this up as there was a break in the circuit, which to be honest, probably made the readings quite good!

It highlighted the problem but only in the same way as the end to end continuity test. It did not help find the break because RI+R2 cross connected at the meter with a break in R2 gives open circuit at every socket on the ring. Linking the 2 N's & 1 cpc (or 2 L's & 1 CPC) was the only way I could think to find the break.

You hit the nail on the head though regarding the IR test and on the basis it was good I went ahead but in future it will make me think.

Cheers, Ron
 
It highlighted the problem but only in the same way as the end to end continuity test. It did not help find the break because RI+R2 cross connected at the meter with a break in R2 gives open circuit at every socket on the ring. Linking the 2 N's & 1 cpc (or 2 L's & 1 CPC) was the only way I could think to find the break.

You hit the nail on the head though regarding the IR test and on the basis it was good I went ahead but in future it will make me think.

Cheers, Ron

Yes good point.

This does go to show however, that any testing is not always conclusive.

At least you found the fault.:)
 
IEE guidance note 3 section 2.7.4 The sequence of tests, sets out the corect order in which tests should be performed.

Regards
 
IEE guidance note 3 section 2.7.4 The sequence of tests, sets out the corect order in which tests should be performed.

Regards

Quite correct and the first on the ring is the end to end continuity.

But also think carefully about the tests and not one of them would help pinpoint this fault, they would only show a fault i.e open circuit. You have to think about ways to locate it and they are not in the book.

Cheers, Ron
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
sunny essex

Thread Information

Title
I.R test before cu changeI
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
tuckermot,
Last reply from
ron55,
Replies
33
Views
4,050

Advert

Back
Top