R
ron55
Hi Ron,
When testing the RFC R1+R2 cross connected at the CU, and then going round all the sockets, this should have highlighted the problem.
An IR test would not pick this up as there was a break in the circuit, which to be honest, probably made the readings quite good!
It highlighted the problem but only in the same way as the end to end continuity test. It did not help find the break because RI+R2 cross connected at the meter with a break in R2 gives open circuit at every socket on the ring. Linking the 2 N's & 1 cpc (or 2 L's & 1 CPC) was the only way I could think to find the break.
You hit the nail on the head though regarding the IR test and on the basis it was good I went ahead but in future it will make me think.
Cheers, Ron