i r testing | on ElectriciansForums

Discuss i r testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Peter Woodford

how do you carry out a live/live test on i.r have done L/N,N/E and L/N all reading greater than 500

cheers
 
A line/line test is only carried out on a 3phase installation where obviously you have 3 line conductors and is tested at 1000V.
 
Hi.

No the line - neutral results only go in the line neutral box. The line - line box is for measurements between phases only.

Terminology is key here, there are four colums for I/R on a full EIC, line - line, line - neutral, line - earth, and neutral - earth.

Nowhere is there a colum for live - neutral or live earth. as old dog has said the live conductors are line and neutral

Hope this helps.
 
do i still need to put the results for l/n in the l/l table then

thanks
sorry peter you have lost me a bit
on the schedule of test result you have insulation resistance.
under that you have a box live/live on single phase that would be line + neutral
on 3 phase that would be between lines + lines + neutral
i hope i am making this clear
what do you have on your paper work if it differs from this
ps
and the box live/ earth
 
Last edited:
sorry peter you have lost me a bit
on the schedule of test result you have insulation resistance.
under that you have a box live/live on single phase that would be line + neutral
on 3 phase that would be between lines + lines + neutral
i hope i am making this clear
what do you have on your paper work if it differs from this
ps
and the box live/ earth


I have live/live and live and earth so I put the live and neutral result in here is this right single phase
 
I have live/live and live and earth so I put the live and neutral result in here is this right single phase
yes mate live/live box line + neutral
live/earth box line +earth
thats it
but for the tests you test as gn3 page 39

why cant they leave things alone live then phase now phase is line if i just keep in mind phase/live/ is line
live can be line or neutral i think i need a cup of tea or coff no no tea
 
Last edited:
gn3 page 39 ? lost me

guidance note 3 page 39 has the proceedure for insulation test
testing with L+N together to earth ect dont want to confuse the post
now we have it sorted but if you have gn3 have a look i am to tiered
i need my cup of tea

so you are ok now with what goes in what box yes ?
 

Reply to i r testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
324
Hi, Do you have the user guide. If not I will put the link at the end of the mail. May be worth checking that the meter has been set for UK usage...
Replies
2
Views
379

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top