Hi I replaced few of the lights 4 to be precise 2 downstairs and 2 upstairs and now my heater won't turn on.
Is it just the coincidence? Did I make a mistake? All the other socket is working but the switch next to the heater won't turn on. I replaced the fuse.. also, if I am correct, light and sockets won't be connected because of different amps . Just need a confirmation or possible solutions.

Thanks
Fish head.
 
Please explain how a spur off a 32a ring circuit is permitted then? It is permitted because the requirements for fault protection are met and overload protection is afforded by the fact that the load is restricted to 2x13a fused loads, =26a maximum. Same applies to the OP's circuit except overload protection is afforded by one, not two 13a fuses =13a.
Reading through this topic again, I do see where you are coming from.
Do you agree with my understanding being, if the OP created a fused spur, at the origin of the circuit in this case, i.e. spurred at the 32A MCB, then the 1.5 T/E is acceptable and in line with OSG H2.3. However if he had removed the ring final conductors from the MCB, the cable and FCU in question is no longer a fused spur on an RFC, and is now a radial circuit, either requiring a 20A CPD, alternatively be wired in 4.0mm T/E, as per Table H2.1
Happy to stand corrected, if I have misunderstood.
 
Thanks for your measured reply. I do not have the BBB to hand for the reg no's but overload protection to any circuit can be omitted if the load is fixed, or if the load is restricted by a downstream device. So if the OP's circuit is a radial serving a single 13a fcu then it will comply on a 32a OCPD as long as fault protection is afforded, which it almost certainly will be. That said same as you, I'd put it on a 16a device, but the advise given to the OP that putting it on a 32a is a safety issue and incorrect is wrong. It would comply.
I'm afraid your comment that a spur from the MCB is a fused spur is incorrect, it's an unfused spur. A fused spur is an extension to a ring circuit spur fed through a 13a fcu, it can serve any number of points on the load side of the fcu
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Swindon
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
I replaced the light and now my heater switch won't switch on.
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
41
Unsolved
--

Advert

Thread statistics

Created
Fishing heads,
Last reply from
fairlight,
Replies
41
Views
5,099

Advert

Back
Top