View the thread, titled "I want a 16 amp socket in the garage with 3 double sockets" which is posted in UK Electrical Forum on Electricians Forums.

I have a 4mm2 armored cable going from the CU in the house, under the drive and into the garage. The breaker for this is a 16 amp type B. I want to have 2.2KW planer machine in the garage that has a 16 amp plug whilst also keeping three existing double sockets in the garage. The three double sockets are currently daisy chained (radial connection?) using 2.5mm2 cable.

Should I have another CU installed in the garage that is fed by the existing armored cable and have the new 16Amp socket on a separate breaker (type C breaker is recommended by manufacturer)? The lighting and sockets could then be on their own breakers too.

Should I (can I) increase the breaker in the house CU and by how much?

Should the socket wiring should be upgraded to 4mm2 as it is not in a ring?
 
Has nobody thought to fit the unshuttered socket in an enclosure which can only be opened with a key and ensure that anyone with access to the key is correctly trained?

Why? Putting the socket inside a locked enclosure defeats the point if. A socket doesn't it? It might as well be a hard wired connection at that point.
 