Hi,
I would like an opinion on two things I am concerned about.
Background.
-----------
I have done some work for a church that has bought a derelict farm. They demolished some of the derelict buildings and put up wood structures on the same footprint in 2012. The builders produced no test cert's and appear to have used the flash bang method of initial testing.
At the meter for the site, there is currently a single phase 100A fuse to feed the whole site (although there is a 3 phase cable buried and in place for when the church want to utilise it). This 100A supply is split by a Henley block and supplies 3 boards (Via Switched Fuses) in 3 buildings. The sub board I have concerns about is in a 2 room Church/Barn in the centre of the complex (the big room can seat 80 people but was outgrown in a couple of years).
My concerns.
------------
1) The board is a 100A plastic RCBO board, and circuits run from this board supply power for 4, 9A space heaters for two tent, 3, 8A urns, an out house with an 8A washer/dryer, 40A supply to a large park home caravan and a supply to a smaller park home caravan as well as lighting to the barn, smaller room and two tents. The caravans have log burners for heat but showers and cookers are all electric. I suspect the 100A Main Switch may be overloaded on occasions for short lengths of time.
If I had done an EICR, I would have coded this as a "C3" and my recommendation to the church when I was working on the farm was to replace the existing CU with a 3 phase metal CU. Even as an adapted single phase supply, the three 100A main switches would never be overloaded. The circuits can be organised so if the 3 phase supply is installed at a later date it is just a change to the intake nothing else needs to change.
2) There is a SWA incoming to the consumer unit, and 5 SWA outputs. The only SWA cable with any support is the incoming cable where there is one attempt to hold the cable in place but it has slipped and several of the SWA cables are pulling on the plastic casing and distorting the casing. This distortion I would code as a "C2". In my opinion, it may be OK and could last many years, or something could give next week as the strain is clear and constant. I have raised this with the church and made them aware few years ago and recommended the 3 phase metal consumer unit more appropriate for SWA terminating.
Reason for this Post.
---------------------
Now, I have moved on and taken a full time job for a housing association, and the church have found an "Old Boy" electrician close to retirement who has looked at the consumer unit and unsupported SWA cables and told them "It's fine, don't worry about it", and don't worry about EICR's.
I would like opinions so I can forward a link to the church site manager and show what the experienced electricians here think.
I would like an opinion on two things I am concerned about.
Background.
-----------
I have done some work for a church that has bought a derelict farm. They demolished some of the derelict buildings and put up wood structures on the same footprint in 2012. The builders produced no test cert's and appear to have used the flash bang method of initial testing.
At the meter for the site, there is currently a single phase 100A fuse to feed the whole site (although there is a 3 phase cable buried and in place for when the church want to utilise it). This 100A supply is split by a Henley block and supplies 3 boards (Via Switched Fuses) in 3 buildings. The sub board I have concerns about is in a 2 room Church/Barn in the centre of the complex (the big room can seat 80 people but was outgrown in a couple of years).
My concerns.
------------
1) The board is a 100A plastic RCBO board, and circuits run from this board supply power for 4, 9A space heaters for two tent, 3, 8A urns, an out house with an 8A washer/dryer, 40A supply to a large park home caravan and a supply to a smaller park home caravan as well as lighting to the barn, smaller room and two tents. The caravans have log burners for heat but showers and cookers are all electric. I suspect the 100A Main Switch may be overloaded on occasions for short lengths of time.
If I had done an EICR, I would have coded this as a "C3" and my recommendation to the church when I was working on the farm was to replace the existing CU with a 3 phase metal CU. Even as an adapted single phase supply, the three 100A main switches would never be overloaded. The circuits can be organised so if the 3 phase supply is installed at a later date it is just a change to the intake nothing else needs to change.
2) There is a SWA incoming to the consumer unit, and 5 SWA outputs. The only SWA cable with any support is the incoming cable where there is one attempt to hold the cable in place but it has slipped and several of the SWA cables are pulling on the plastic casing and distorting the casing. This distortion I would code as a "C2". In my opinion, it may be OK and could last many years, or something could give next week as the strain is clear and constant. I have raised this with the church and made them aware few years ago and recommended the 3 phase metal consumer unit more appropriate for SWA terminating.
Reason for this Post.
---------------------
Now, I have moved on and taken a full time job for a housing association, and the church have found an "Old Boy" electrician close to retirement who has looked at the consumer unit and unsupported SWA cables and told them "It's fine, don't worry about it", and don't worry about EICR's.
I would like opinions so I can forward a link to the church site manager and show what the experienced electricians here think.
Attachments
-
20160601_102717.jpg134 KB · Views: 79
-
20160601_102724.jpg145.1 KB · Views: 77
-
20160601_102733.jpg109.5 KB · Views: 75
-
20160601_102740.jpg95.9 KB · Views: 76
-
20160601_102749.jpg132.4 KB · Views: 72
-
20160601_163011.jpg79.6 KB · Views: 71
-
IMG_6386.JPG112.9 KB · Views: 70
-
IMG_6387.JPG122.4 KB · Views: 69
-
IMG_6389.JPG137 KB · Views: 68