No they’re not. I’ll check the make when I empty my van tomorrow.No, is your pic Fern Howard.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss I'd rather install Ikea light fittings in the Lighting Forum area at ElectriciansForums.net
No they’re not. I’ll check the make when I empty my van tomorrow.No, is your pic Fern Howard.
Not enough room to get 4x 3 way Wagos in the fitting without them applying pressure to the PCB.
Just in case you've not seen these smaller sized Wago connectors - super slimNot enough room to get 4x 3 way Wagos in the fitting without them applying pressure to the PCB.
Unfortunately we have to get the lighting as close as possible to the ceiling as people need to install various cables etc in the overhead steelwork. This also stops us from using Kliks and flex as they may get ripped out accidentally.Could you not have mounted the fitting on a besa box? As then your joint can be in the besa box with a flex the the light fitting and you also keep your steel conduit continuous.
Plus it makes it easier to replace any fitting which may fail in the future.
Because the project team went out and bought a couple of thousand lever type and wont buy any new ones until those are wasted out.Just in case you've not seen these smaller sized Wago connectors - super slim
Compact Push Wire Connector 2.5mm 3 Pole - https://www.tlc-direct.co.uk/Products/WA203.html
Unfortunately we have to get the lighting as close as possible to the ceiling as people need to install various cables etc in the overhead steelwork. This also stops us from using Kliks and flex as they may get ripped out accidentally.
View attachment 41839
These are fed via conduit from the far end. TBH I'm going to suggest we go back to 6' battens as these bulkheads are proving to be too much hassle.
Are they metal bulkheads? If not how are you earthing each piece of conduit?
If such a low profile is needed install the fittings next to the conduit connected via a tee box.
Conduit is earthed by mechanical connection to the metal roof and tested back to the MET.
Only a continuity test, not ideal by any stretch. The site has DC sensitive equipment so any other form of testing is a non starter.What makes the connection to the roof? Do you test it with something like a duct or or just a low current continuity test?