Afternoon everyone..

During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the main consumer unit in the house to a garage consumer unit. The poor readings are not on the outgoing circuits in the garage.

There must be a join somewhere as it is T&E leaving the main CU and then SWA entering the garage CU. I cannot find this join.

The length of run is very approx 40m (as I don't know the course it takes underground). It is below many paving stones, and various other obstacles. It would cost a lot and cause major disruption to run a new cable so I am considering how to find the fault area. It's a difficult choice as it could takes days of fault finding and perhaps cause even more disruption than a planned route for a new cable.

One thought is to use an ezicat 100 cable finder to at least work out the route of the cable and then dig in certain areas (that are easier to get to). Then perhaps cut the cable and test both ends to see which I can keep in situ and which needs further investigation. I have never used an ezicat 100 before, are they reliable? Would this be a situation where it is the right tool for the job?


Thanks all.
 
Overhead?
Speak to anybody that’s dug up the ground for water mains…. They probably nicked the cable with a digger bucket
If the SWA cable was steel armored, I have pulled an extremely long cable out of the ground with a mini digger.
The problem would be connecting the new cable to the old cable so it could be pulled through without breaking.
You can make a good connection between the L/N/E but that is not good enough, you would need a 2 part epoxy resin for metal and using the section of 400 mm outer sheath swa cable, cut a 20mm section slit out all of the way down the 400mm piece so you could apply the resin.

That holds it, all you need then is a mini digger one end
 

Ps, just for reference , If you see any watermains people, (not going to mention names) but the guys digging up the watermains.

It's worth chatting to them because they'll mole it for you, a lot cheaper and quicker than you think.
Ha ha, I like the way the mole appeared right on cue in the right place. It might work in some soils, but around here it could go anywhere after it's been diverted by a rock, or two, or three, or ...
I remember a few years ago I was doing a network install for a client on a new development. Outside there was a guy trying to mole across the site access road - it wasn't fully surfaced, but he was trying not to disturb what was down. When I was leaving, he was digging a hole hoping to find his mole which hadn't gone straight across as it was supposed to.
 

Reply to Ideas for finding fault area in underground swa? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top