Hi All.
Its been ages since I have been on here- Fortunately log in details stored on PC.
I have just had a new boiler and 210 ltr unvented tank fitted in the loft to replace a very old Baxi back boiler. I have now fitted a Solic 200 diverter to utilise all the spare capacity from the 3,84 Kw Pv system on the roof. This has only just become an option as the old existing tank did not have an element fitted and I was told that the chances of fitting one to the old tank without damaging it were slim to none!
The issue that I have after checking the element fitted to just below the middle of the tank is that the thermostat appears to cut out a lot earlier than I expected. According to the manufacterers website, the element should when turned to maximum, cut out at 70deg/C, having a red tag although on the cover of my element, it states 65deg/C
As the sun is out today, I have had a bath rather than the normal shower and the water has been heating via the diverter for 90 mins or so and has taken 3.23Kwh of power but has now cut off due to the thermostat on the element.
Having done some very rudementary checking with a meat probe which does measure 100deg +/- when put in a boiling kettle, the hottest point on the hot water take off pipe and also under the nearest hot tap after running off some water is 50deg/C
Obviously, I have checked that the immersion stat is set as high as possible so would it be fair to assume that the thermostat is not acting correctly and is cutting out prematurely and would I have reasonable grounds to contact the fitters/ manufacterers and request a replacement element?View attachment 110936View attachment 110937
Its been ages since I have been on here- Fortunately log in details stored on PC.
I have just had a new boiler and 210 ltr unvented tank fitted in the loft to replace a very old Baxi back boiler. I have now fitted a Solic 200 diverter to utilise all the spare capacity from the 3,84 Kw Pv system on the roof. This has only just become an option as the old existing tank did not have an element fitted and I was told that the chances of fitting one to the old tank without damaging it were slim to none!
The issue that I have after checking the element fitted to just below the middle of the tank is that the thermostat appears to cut out a lot earlier than I expected. According to the manufacterers website, the element should when turned to maximum, cut out at 70deg/C, having a red tag although on the cover of my element, it states 65deg/C
As the sun is out today, I have had a bath rather than the normal shower and the water has been heating via the diverter for 90 mins or so and has taken 3.23Kwh of power but has now cut off due to the thermostat on the element.
Having done some very rudementary checking with a meat probe which does measure 100deg +/- when put in a boiling kettle, the hottest point on the hot water take off pipe and also under the nearest hot tap after running off some water is 50deg/C
Obviously, I have checked that the immersion stat is set as high as possible so would it be fair to assume that the thermostat is not acting correctly and is cutting out prematurely and would I have reasonable grounds to contact the fitters/ manufacterers and request a replacement element?View attachment 110936View attachment 110937