B
bobodhi
Hi, I've been asked to go look at an immersion heater which isn't working.
I haven't looked at one before and would appreciate a heads up.
Obviously there may be a problem with the power supply or the unit may be faulty.
Would appreciate any comments by those with experience as to a suitable approach to the problem.
Cheers, Kevin
Check for supply at element, bypassing the thermostat if necessary. If supply there = faulty element
Very common for some of the older types of immersion to trip RCBO's straight out e.g. when 17th Ed CU fitted (had 10 out of 40 OAP flats do this on a single job!).
As above most likely is the element so test for supply to element first and if thats ok test element hopefully problem solved.
Chris
Hi, thanks for the reply, just a quickie, best way to test element and expected readings if faulty or not.
Also, how easy is it to remove and replace the element if it is faulty? Do I need to do anything like drain the tank etc?
Cheers Kevin
get a spark to test it you will ned to isolate it and drain tank then put new one in if found faulty but a spark will be best placed to test it for you
Test the element line to neutral on continuity and you should read resistance of roughly
3,000 W / 230V = 13.04A
230V / 13.04A = 17.64 Ohms
Hope that helps.
If the element is shot it may be open cicuit
Immersion heater faulty
Australia
bobodhi,
bobodhi,
TrueNAS JBOD Storage Server