hi all need a bit of advice on an immersion heater fault.

attended site yesterday to an immersion heater circuit that blew the fuse 15A (3036) as soon as it was inserted.

tested insulation res on cable (1.5t/e) and very low reading so this morning run a new 2.5t/e in up to double pole switch in airing cupboard.

connected up and everything worked fine until i went out to the garage where cu is and there was a very fishy smell and fuse holder hot to the touch.

when i removed the fuse there is burn marks to the back of it but fuse wire still intact.

system is tt with 3036 rewirables and in good condition.

immersion heater reading 15.7 ohms across terminals but looks like it wil be a bugger to remove and inspect.

all advice welcomed please :eek:
 
Last edited:
Must admit, i wouldnt waste too much time on it.

Just replace the immersion, it could work out cheaper for the client in the long run, especially if spend much more time on it.

All IMO.
 
Do you know that it isn't something like a loose or high resistance connection at the fuse or fuse holder? that would cause it to heat up too you know? ....
just another option
hi stretchy,
not sure what you mean :confused: i have replaced the cable and my connection is fine

Must admit, i wouldnt waste too much time on it.

Just replace the immersion, it could work out cheaper for the client in the long run, especially if spend much more time on it.

All IMO.
thats what i would do too jason but it looks like its going to be a bugger getting the old one out and theres a good chance the cylinder will get damaged :eek:
 
Last edited:
If its rewirable would check the push in connections at the board, terminals are probably checked by you anyway. If its a new element who fitted it and is there water in the immersion ? Just a thought.
 
I woult think the element I replaced one last week.jTo remove it just get an immersion element box key which is a big hexagonal (after draining the tank) with a bar for leverage.If it won't unscrew bang the end of the bar with a bit of 2x4 wood or similar.Got to be careful as the tanl is soft copper and the immersion insert is sometimes soldered in.
 
I woult think the element I replaced one last week.jTo remove it just get an immersion element box key which is a big hexagonal (after draining the tank) with a bar for leverage.If it won't unscrew bang the end of the bar with a bit of 2x4 wood or similar.Got to be careful as the tanl is soft copper and the immersion insert is sometimes soldered in.

Dont drain the tank until you have cranked the immersion hex loose. Whilst filled with water it greatly helps to keep the tank from distorting, obviously once you have freed the element drain off tank, and dont worry a quarter turn wont make the element any less water tight, but using this method could save you damaging the soft copper on the tank;)
 
I woult think the element I replaced one last week.jTo remove it just get an immersion element box key which is a big hexagonal (after draining the tank) with a bar for leverage.If it won't unscrew bang the end of the bar with a bit of 2x4 wood or similar.Got to be careful as the tanl is soft copper and the immersion insert is sometimes soldered in.
hi sparkdog,
ive changed a few immersion heaters in my time, but this ones a bugger. tried moving it and it doesnt want to know. dont want to strip the neck out of the cylinder :eek:

i reckon it can only be the immersion itself as ive renewed the feed im just a bit concerned why the fuse doesnt blow instantly now instead of warm itself up in the cu to the point where it would probably catch fire :eek:
 
It's because its a bugger that your hoping the problem lies elsewhere, but to be fair I think a new element is going to be needed, as said you could try a clamp meter and see what the circuit draws, And also check those connection from the consumer lugs to the prongs on the fuses. Very best of luck to you mate I am sure it will shift eventually. Dont forget to leave the tank filled until the hex shifts, it really does help.;)
 
It's because its a bugger that your hoping the problem lies elsewhere, but to be fair I think a new element is going to be needed, as said you could try a clamp meter and see what the circuit draws, And also check those connection from the consumer lugs to the prongs on the fuses. Very best of luck to you mate I am sure it will shift eventually. Dont forget to leave the tank filled until the hex shifts, it really does help.;)
cheers baldsparks. could be changing the cylinder when it strips then :eek:
 

Reply to immersion heater problem in the Australia area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top