Thanks - that's really interesting. Just one point though: elements in dishwashers etc are not limited to 1kW (my dishwasher element's the best part of 3kW [though it is old]; washing machine about 2kW; oven in total >3kW but interestingly it staggers the switching of its elements). However, they are not controlled by burst firing so they will only cause intermittent flickering as they switch on and off infrequently, rather than constant flickering by being switched several times a second.
I think it's the newer models that have smaller elements, and use the burst fire just to keep them topped up with heat, probably as they use so much less water and lower temps... not my field though, but I have stuck power meters on a few in the past to see what they're drawing.
 
Oh I see - so they have smaller elements in order that they can use burst firing? With solar panels, good reason to get a new dishwasher!
 
Hi GavinA,

Thanks for the detail, it must be down to some of the characteristics of the individual installation, as I say we have had no reported problems at all. Reading the documents you posted, I wouldn't be suprised if some of the supplies don't meet those specications!
 
Thanks Gavin A for the information. So where does this leave us? I have a burst fire model and a phase angle unit running, both work really well. Has anybody come up with suitable filtering for the phase angle cutting? I have used commercial two stage units , but I don't have any specific equipment to test if it is below the regulation amount of interference.
 
Hi guys,
Just had a look at latest comments on ths thread as I have now more or less dropped out of Controller market (4 left in stock if anyone interested) but this latest batch confirm my comments 6 months ago that no-one will be able to legally market a cheap proportional control due to harmonics, etc.
Hence why I was marketing the SolarHeat which was simple fixed switching but not the most efficient.
Did echase manage to get his design commercially developed?
 
Did echase manage to get his design commercially developed?

Yes. My non-burst fire unit meets EN 61000-6-3 Electromagnetic compatibility (EMC). Generic standards. Emission standard for residential, commercial and light-industrial environments 2007, and BS EN 61000-3-3:2008 and EN 61000-3-11 for flicker.

I suspect the original EMMA device did too although I believe their more recent devices use high frequency pulse width modulation, which reduces the low frequency end but increases the high frequency so you need a screened cable to the immersion.
 
ah, hold on they're different regulations, it's BS EN 61000-3-3:2008 and EN 61000-3-11 that are the regulations in question.

this diagram explains why the Immersun can't meet those regulations, as it shouldn't be able to cause a volt swing each time it cuts in of more than just under 0.3% or around 0.7V, but the location we had it at I measured around a 2V drop from switching on a 3kW load, so effectively every time the burst fire kicks in on each cycle it's causing around a 2V drop on that cycle.

Presumably this is why dishwashers and washing machines are restricted to around a 1kW element.

[ElectriciansForums.net] Immersion Heater - PV electricity





Design for EMC Part 6: ESD, dips and dropouts, etc.

http://www.reo.co.uk/files/handbook_en_61000-3-3_and_en_61000-3-11.pdf

I've been meaning to get back to 4-Eco about this tbh.

Excellent summary of the problem. I have built a couple of experimental burst fire controllers and installed them in 2 different houses. In both there was a significant level of lighting flicker, including neighbour’s lights, so I had to rapidly disconnect them. These were not houses at the end of long wires to the substations.

As I understand it you might be able to slow down the flicker to a frequency that is to the left of that graph and hence just about meet the standard at 3kW but it will be so slow that it won’t spoof the electricity meter into recording a zero export/import in all circumstances and certainly not when new/smart meters come in with the likelihood that they will be more sensitive to catching short bursts of power.

Also if you go too slow you may meet the standard but your neighbours will still see their lights flickering fast enough to be annoying.

The trouble with EMC etc. standards are that they are quite severe so it may be that you have failed even if you don’t see the flicker. Some houses might have impedances low enough so that no one notices the flicker, especially if you are not looking for it, but actually be producing voltage dips more that that graph allows.

One has to ask the question “Why do cooker and dishwasher manufacturers with all their research resources limit their burst fire controllers to 600-1000W?” It is because they can’t comply with flicker specs at higher powers. As they can’t what chance have we?
 
Agreed. The only point I would take issue with is if newer meters would in fact be more "sensitive" to small reverse power flows, given that I don't see why there would be a technological limitation on the ability of current meters to detect this. I would have thought that installing a meter that behaved differently for no good reason would be unfair. Is the curious way the current ones work an attempt to make them behave more like analogue meters? I don't know - pure conjecture!
 
In a not very scientific test I measured a 2 volt drop on my house with a DMM by turning on a 3kW kettle on and measuring the change in voltage at the consumer unit. I am only 200m and 16 houses from the substation. Using that figure (= 0.9%) and the above graph it shows that the switching rate has to be less than about 100 changes per min or 1.6Hz. That is probably too slow to definitely spoof a meter and has to be much slower at non 50/50 mark space ratios (half power). My friend’s was running at a “legal” 1Hz when the neighbour complained. Would stress though that this is in no way taking electricity one has not paid for, as it is returned again.

But before outright saying all faster burst fire 3kW devices fail it has to be said the proof is in an actual flicker test in a lab, as that graph is only an interpretation of the flicker standard from http://www.reo.co.uk/files/handbook_en_61000-3-3_and_en_61000-3-11.pdf and probably only applicable to 50/50 mark space ratios, which for a solar diverter is rarely the operating point. Someone may yet prove us wrong by managing to meet the spec whilst also stemming the neighbours’ complaints.
 

Reply to Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

Similar threads

  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
158
By the time you've dealt with isolator valves that won't shut off and drain valves that won't open, half a day will be gone before you've removed...
Replies
5
Views
715

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks