I went to a job that the owner felt was a bodged job. It was basically a radial circuit wired at the start in 4.0mm T&E, and then it goes to a few sockets that is supplying a washing machine and tumble drier. From there it goes upstairs to the airing cupboard where it feeds a single switched socket that the owner has to swap either the immersion or his shower pump, and then the circuit goes up to the loft where it feeds the boiler. All the wiring apart from the first leg of the radial is 2.5 T&E and fed from a 16amp MCB 60898

I was always under the impression that from the 60's immersions were on dedicated circuits and in most cases fed off of a DP isolator.

I rang Napit and they have said that although its bad design its doesn't breach any regs and that in an EICR it could only be coded a 3 as it is on a radial and not a RFC.

This doesn't sit well with me as it goes against everything I have been taught and told to date.

Opinions please
 
As said bit rough but not dangerous, surprised its doesnt overload, must have to use each appliance on its own

immersion circuits usually start out 'dedicated' but often end up with shower pumps and all sorts of other things connected to it

not really a big issue
 
16A circuit too small for the job though - immersion and either of the large appliances exceed 16A for starters. It'll probably work but bad design.
 
Many, many Immersions are on plug tops off socket circuits - and that was OK back then.

Sure we wouldn't do it that way now, nor would we fit air bags to the Mk 1 Mini (the original version)
 
I went to a job that the owner felt was a bodged job. It was basically a radial circuit wired at the start in 4.0mm T&E, and then it goes to a few sockets that is supplying a washing machine and tumble drier. From there it goes upstairs to the airing cupboard where it feeds a single switched socket that the owner has to swap either the immersion or his shower pump, and then the circuit goes up to the loft where it feeds the boiler. All the wiring apart from the first leg of the radial is 2.5 T&E and fed from a 16amp MCB 60898

I was always under the impression that from the 60's immersions were on dedicated circuits and in most cases fed off of a DP isolator.

I rang Napit and they have said that although its bad design its doesn't breach any regs and that in an EICR it could only be coded a 3 as it is on a radial and not a RFC.

This doesn't sit well with me as it goes against everything I have been taught and told to date.

Opinions please

The customer is clearly not happy with the situation as it stands.... So more to the point, what are YOU now intending to DO with this radial circuit??
 
The customer is clearly not happy with the situation as it stands.... So more to the point, what are YOU now intending to DO with this radial circuit??

This is the problem, as its not a dangerous situation, but bad design in my opinion. I have stated this and left it with the customer as bringing the circuit in line with good practice will require carpets up etc.

If this was a C1/C2 then it would be an entirely different conversation.
 
Why were you at the property?
Were you there to carry out an EICR?
Or
Were you there because your client wants this bodge improved?

I was originally asked to fix a fan and look at putting the shower pump on a separate circuit as the property is a rental and the landlord knew having to keep swapping the plugs to have a shower or hot water was not ideal.

After verifying if there was an aerial booster on the lighting circuit, I ruled out putting the pump on the lighting circuit and found that the boiler was also run on the radial circuit that supplies the immersion/pump.

The customer just wanted to have the pump and immersion hard wired.
 
Ok, so why all this talk of EICR codes if you are not doing an EICR?

If the job is to hard wire the pump and IH then work out the best way to do this and crack on with it (after agreeing price etc)
If there is a boiler in there then the immersion is presumably only there as a backup in case of boiler trouble? In which case you could open up the ring circuit to feed it, the pump and the boiler.

Why did having an aerial booster connected rule out putting the shower pump on the lighting circuit? Surely the fact that it is a lighting circuit should have ruled it out without any further questions ?
 
Why did having an aerial booster connected rule out putting the shower pump on the lighting circuit? Surely the fact that it is a lighting circuit should have ruled it out without any further questions ?

What's wrong with connecting a power shower to a lighting circuit?
 
Why would it be an issue just for being the light circuit? Having 2 things on lighting circuit, then that is the difference.

I used the C3 point as that is the way Napit told me to justify it. Its not breaking any regs and its not dangerous, but it is bad design.
 
How do you define a 'thing' in this instance? And why can you have one connected to a lighting circuit but not 2?

Forgive me if I am being simple but surely the clue is in the fact it is a lighting circuit! That is to say it is a circuit for lights!
Maybe I am wrong but I was taught that it is bad practice to connect unrelated equipment to a lighting circuit.
When you have been asked to fix one bit of bodgery it some somewhat inappropriate to fix it by bodgeing a supply from the lighting circuit.


What do you need to justify? And to who? The customer has asked you to connect the items to a hardwired connection so why do you need to justify to them the need to do this?
 

Reply to immersion on a non dedicated radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
899
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
166

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top