Testing a domestic ring main recently R1 end to end was .4 Rn was .4 the cpc which was probably 1mm (oldish cables 1975ish) read .2. possible reasons for this??

On another issue how do test the loop impedance at a fixed appliance or a light, to fulfill the measured loop impedance column requirement on the schedule of tests. will the calc R1 + R2 suffice?
 
At the Consumer unit I split the ring and test end to end on all 3 legs I would have expected the CPC to have a reading of about 1/2 again due to the smaller csa
 
I always use guidance notes 3 for testing explains and shows how all testing should be done, i have noticed i always get different readings if i test again and always make sure the meters test leads are making a good connection.
 
At the Consumer unit I split the ring and test end to end on all 3 legs I would have expected the CPC to have a reading of about 1/2 again due to the smaller csa

Me too about 1.67 times. Everything unplugged?

If a higher reading is found then I'm afraid further investigation is required to check its a fall ring, no inter connections, any connections, breaks etc.

The loop Zs is taken at the furthest point of the circuit and to do the test you will have to check your instructions for your own meter as some require a two lead connection and others three. You should also check to see your meter has a D-lok to avoid nuisence tripping of RCD's.

PS as Fog has said GN3 is your best bet.
 
The reason for a difference resistance reading (ohms) between the live conductors and earth, is the simple fact it is smaller in CSA. Rather than having a guess, like you said, half it.. what you should do is a simple calculation. For example on a ring circuit the line conductors are usually 2.5mm and 1.5mm for cpc.
To calculate this, you basically 2.5/1.5 = 1.666. So the CPC resistance should be roughly 1.666 times greater (in theory)

Hope this helps...
 
Thank you all , however the reading for the cpc is lower not higher, I would expect to to find the cpc come in at about .66 not .2 which is what I'm reading. I will check to see if everything is unplugged but if its split at the consumer unit I cannot see if an item plugged in would make that much difference to the cpc impedance
 

Reply to Impedance readings on a ring in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
884

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top