SparkusMaximus
lol, I wonderd what I had said to give the 80m, yes I would like to go 10mm 3 core for 15m on a 63a but was thinking I might need a 80a with a 16mm.
Hi all,
My mother in law has a gagarage converted into an annex, a lot of bodging has taken place all before I knew them.
Inside the flat conversion we have a 9.5 kw shower on a 32a, a ring on a 32, light circuit on a 6a and a water heater on a 16a,
Now the SWA supplying this is 6mm protected by a 32a mcb on the rcd protected side of the CU.
I said I would sort it out for them as when they have the shower it will trip sometimes as they use a plug in heater.
I want to obviously change the cable, but working out my MD its looking like I need a 16mm this will be a nightmare so can 10mm be justified?
CC of 10mm swa ref method C is only 58a table 3 (three core as I need to transport the earth)
Do I need 16mm or will 10mm sufice.
Thanks guys I really appreciate your help as I want to be able to work things out the BRB way.
Should we not be addressing other things in this post ie why we have an inductive load of nearly 42amps on a 32amp MCB. That should be addressed first off. So unless that is wired in a 10mm^ cable he may find that fitting the correct protection device for the load be another issue to deal with.
No diversity allowed for showers!
not sure if I understand what your getting at but I have stated its bodged, and I said I would rectify it, I am asking if 10mm would be suitable or do I need to go bigger. There are numerous bodges, but this one is the one I can't work out the size of cable needed, as I work it out to need a 16mm but I am hopping that I have done something wrong and can get away with 10mm.
50 Amp MCB fromthe DB .
40 Amp for the shower,
16 Amp for the sockets
16 Amp for the heater,
6 Amp for the lighting,
will be fine
main cut out 100, 63 main switch, however if I go for 63a I Will put in 1 way board more than likely, but didn't think about that I don't think I can put a 63mcb in with a 63 main fuse can I.
Thanks very much MrEnigma for you help here, much appreciated.
What is the main switch size at the DB 100 or 63?, and more importantly what have the DNO supplied at the head?