I have just been to look at a job where i was asked to install a cooker as the previous one had nearly burned the house down apparently. when i took the cooker out there was a large burnt patch (300m accross), loads of charcoal, almost got through 1/2" ply below . when i pulled out the heat resistant flex i couldn't see where it had been plugged into, but it's likely it was plugged into the ring. it is a 3200W cooker from argos, the customer had got an argos technician out and apparently the cookers fine and it was down to the installation. customer reckons it was sat ontop of the connections and it was bodged up, I did try asking the customer to clarify how the cooker was connected up, but couldn't get much out of her! theres a 2.5 T&E running below the worktop behind the cupboards, not connected to anything but still live? but couldn't find where it came from as all the cupboards are full to the brim!

it's only a small house, 2 up 2 down, it's TT, got a 100mA RCD upfront and a 8 way 3036 board with 3 circuits (ring, lights and shower). ZE is 5-6ish ohms. would it be ok to spur it off the ring to a fused spur above the worktop, and then down to the cooker? an just put it on a minor works?
I'm not entirely sure what the line is about working on a circuit without 30ma RCD protection, do i need to add an RCD first or not?

also, the voltage is 250V at this house, 3200W at 250V is 12.8, so it i put a 13A fuse in the FCU then it will be alright? i seem to remember something from college saying all calculations to be worked out at 230V, in which case the current will be 13.9A and it will be more than the fuse rating. probably never blow, but what should i do here?
 
Any NEW sockets, or wiring that is concealed within the walls requires 30ma RCD. So if you use an FCU and your wiring is surface mount then I don't see a problem. The cooker will probably never pull full load anyway and 13.9 amps won't blow the 1361 fuse for ages. If you're worried use 4mm cable for the spur.
 

Reply to in after a cowboy, cooker nearly burnt the house down! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top