ExArmy

-
Joined
Jul 27, 2010
Messages
716
Reaction score
143
Location
cumbria
I have just been to look at a job where i was asked to install a cooker as the previous one had nearly burned the house down apparently. when i took the cooker out there was a large burnt patch (300m accross), loads of charcoal, almost got through 1/2" ply below . when i pulled out the heat resistant flex i couldn't see where it had been plugged into, but it's likely it was plugged into the ring. it is a 3200W cooker from argos, the customer had got an argos technician out and apparently the cookers fine and it was down to the installation. customer reckons it was sat ontop of the connections and it was bodged up, I did try asking the customer to clarify how the cooker was connected up, but couldn't get much out of her! theres a 2.5 T&E running below the worktop behind the cupboards, not connected to anything but still live? but couldn't find where it came from as all the cupboards are full to the brim!

it's only a small house, 2 up 2 down, it's TT, got a 100mA RCD upfront and a 8 way 3036 board with 3 circuits (ring, lights and shower). ZE is 5-6ish ohms. would it be ok to spur it off the ring to a fused spur above the worktop, and then down to the cooker? an just put it on a minor works?
I'm not entirely sure what the line is about working on a circuit without 30ma RCD protection, do i need to add an RCD first or not?

also, the voltage is 250V at this house, 3200W at 250V is 12.8, so it i put a 13A fuse in the FCU then it will be alright? i seem to remember something from college saying all calculations to be worked out at 230V, in which case the current will be 13.9A and it will be more than the fuse rating. probably never blow, but what should i do here?
 
the very last sentance on that page says " the remainder of the installation would require protection by a 100mA rcd"

which implies not every circuit must need 30mA rcd for it to say that ??

not much gratitude there for walking you through your job exarmy ? :-/
 
the very last sentance on that page says " the remainder of the installation would require protection by a 100mA rcd"

which implies not every circuit must need 30mA rcd for it to say that ??

not much gratitude there for walking you through your job exarmy ? :-/

sorry if that came accross as me not showing gratitude, i am greatful for all input on this thread and wasn't arguing with you, but i just can't see how page 28/9 clearly lays out the requirements, to me it's consfusing! for a start it says "TT conduit installations". i've had a good poke about the house, not seen any conduit yet. so does that apply?
 
It doesnt matter what sort of wiring the house has , even if it is in steel conduit or not.
Its only your work that has to be considered , so if you install a cable to your new cooker spur , that has to be 30mA rcd protected , which will mean fitting a rcd at the mains even though theres a 100mA rcd already there.
OR
Fit the new cable in surface trunking then you dont have to fit extra 30mA rcd.
 
It doesnt matter what sort of wiring the house has , even if it is in steel conduit or not.
Its only your work that has to be considered , so if you install a cable to your new cooker spur , that has to be 30mA rcd protected , which will mean fitting a rcd at the mains even though theres a 100mA rcd already there.
OR
Fit the new cable in surface trunking then you dont have to fit extra 30mA rcd.

I agree with surface mount otherwise you may find yourself having to work around discrimination issues.
 
Hi sorry to butt in,

As the cooker is classed as fixed equipment and is over 2kw shouldnt it be on a dedicated radial. Thats just my take on it so please dont shoot me.

Also as its now on its own dedicated radial it will need 30mA RCD protection because if you surface mount it it will look awful and you will get the name John Wayne.
 
As awful as surface mount is it does serve it's purpose and it's the easiest option for the homeowner to consider.

I think we have all probably installed surface mount at some stage or another? :thumbsup
 
is there something that says fixed equipment over 2KW has to be on a dedicated radial? it's just that i wouldn't know how to justify that to the customer, it's only 3.2KW, almost the same as a kettle!

and regarding surface mounting to avoid having to fit RCD, ihave just come accross Reg 411.5:

"cables installed on the surface do not specifically require RCD protection, however, RCD protection may be required for other reasons, for example, for the fault protection, where the earth fault loop impedance is such that the disconnection time for an overcurrent device cannot be met"
 

Reply to in after a cowboy, cooker nearly burnt the house down! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top