inadiqate bonding from the consumer | on ElectriciansForums
Discuss inadiqate bonding from the consumer in the UK Electrical Forum area at ElectriciansForums.net
buzzlightyear
Nearly Esteemed
star command
been to price up a job, customer just has just moved in, the requirement was a couple replacement of lights ,new security light.
I asked the customer that I need to see the c/u and check the main earth bonding.
looking at c/u the main bonding to the MET .wait for it was two 6mm earths
from the c/u to the MET . water & gas 10mm. flipped the lid down on the c/u and to see what the MCBs are on any RCDs not one.
the customer says the place was rewired in 2006 .any paper work for that ,at the solicitors the customer says .
I then told the customer you need to speak to your solicitor .
I was then told by the customer I have property's rented out and have c/u like that .like victor melldrew I don't believe it.
having spoken about the security light going out side the back door
the customer said I will get that of flebay only about ÂŁ20 quid
you will fit it she said .I will fit it but their is no warrantee on you supplying me with that .customer saying warrantee from flebay .
f77king customers what do they know.
rant over
I’m confused, is the protective bonding in 10mm and the earthing conductor is 2x 6mm cables in parallel?
Plus is the MET not the earth bar inside the consumer unit?
Feel your pain Buzz. I went to house to look at moving 2 sockets as a recommendation. Straight forward job, so did a quick Zs on the existing sockets and got 14Ω :eek: Then after checking all the terminations on the sockets on the ring and did it again and got 1.9Ω.
Went to CU and opened it up :eek::eek::eek: what a mess!!! Did a Ze test and got 1.9Ω on the TN-S. The customer then piped up and said 'Oh we had a problem a couple of years ago with something in here. Our previous electrician did some work to some other sockets and then when he tested the board he was having problems. He made a phone call and some guys came out and messed around with something and said I didn't have to have my drive dug up and that it is all ok'. I asked if there was any paperwork relating to this previous work and they said no.
I'm now waiting for western power to sort it out. I expect to see a new electrode in place. Wasted an hour of my life for no reward.
Oh, the main earth was 16mm and the gas and water were 16mm also......
I was always taught that the MET was the metal connector block outside of the consumer unit which has the DNOs incoming earth connected to it. Gas and water bonding is connected to this also and an earth cable is run into the consumer unit from this block. We dont place a Main Earth Terminal do not disconnect sticker inside a consumer unit.
I was always taught that the MET was the metal connector block outside of the consumer unit which has the DNOs incoming earth connected to it. We dont place a Main Earth Terminal do not disconnect sticker inside a consumer unit.
It can be either a standalone terminal or inside a DB, see the definition of an MET in 7671. A label is only required if the MET is separate from main switchgear
Reply to inadiqate bonding from the consumer in the UK Electrical Forum area at ElectriciansForums.net
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
2 3 4 5
6K