H

highspark

Doing a CU change in a flat, concrete floors and ceilings, just been decorated in hallways and bedrooms. Basically kitchen fitters ripped units out today and the bonding to the main gas has been cross bonded to the water behind units. Water is bonded back to the MET. However incoming water is bonded in a cupboard next to CU (nowhere near kitchen). There is absolutely no way I can get 10mm bonding back to the board without smashing hell out of the place!

Do I need to get this back to the MET or can I note on cert it's cross bonded! Absolute nightmate!
 
Can you join the gas bond to the water bond with a through crimp so it is one continous cable from the MET to both and it is unbroken?
 
It needs bonding either back to the MET, EMT if earthing conductor is adequate for bonding or joined on to the water bond either at the clamp or via a through crimp.
 
No, basically main water is bonded next to the front door - goes through a riser to each flat. The boiler (along with gas meter) is in the kitchen. 10mm bonding from gas pipe to the cold on the boiler.
 
If it's TNCS I'd say you have no choice but to bond the gas in 10mm back to the MET. TNS you might consider the current arrangement satisfactory assuming it tests OK,and write it as a departure. Your call on that,your name on the cert.
 
I would not be too concerned at all on this.Bear in mind, you did not install this bonding, so you are not initially verifiying it. You can only check / test it as you would an EICR.Use long lead test to confirm a sound connection between MET and the cold pipe you speak of. Ensure BS951 tags are present on earthing clamps. It is still effectively bonded just not exactly to what the non statutory document would like. Note on cert. No worries.
 
Problem is other spark/kitchen fitter is telling customer it needs to go back to CU! That's the problem here! I can't be bothered going back and forth with the other spark because ideally it should go back to CU! Customer wants me to do the work as she fears Kitchen fitters will over charge!
 
Problem is other spark/kitchen fitter is telling customer it needs to go back to CU! That's the problem here! I can't be bothered going back and forth with the other spark because ideally it should go back to CU! Customer wants me to do the work as she fears Kitchen fitters will over charge!

If she's willing to pay crack on...
 
Problem is other spark/kitchen fitter is telling customer it needs to go back to CU! That's the problem here! I can't be bothered going back and forth with the other spark because ideally it should go back to CU! Customer wants me to do the work as she fears Kitchen fitters will over charge!
Hell would freeze over before I ever took on board electrical advice from a kitchen fitter. Who is writing the cert, you or kitchen fitter?
 
I might be misreading the setup, but if the water bond is ok, then there is not a problem with through-crimping the existing bond and extending to the gas (as Leesparky has said)
 
I know what to do here. Install a bonding clamp on gas pipe with a short piece of 1mm connected to it. Tell kitchen fitter it is an aerial for your wireless bonding arrangement back to MET. He will definately believe you as he does not understand electrical type stuff thingys. Then tell customer it is free. Everyone will love you.
 
If there's 'negligable impedance' between the bonded cold water main near the CU and the cold feed in the kitchen [i.e. the same pipework with no plastic in between] then from a common sense point of view it will be absolutely fine. As TJ Anderson has said just note it on the certificate and hide that one from the assessor when he next turns up. :p
 
I know what to do here. Install a bonding clamp on gas pipe with a short piece of 1mm connected to it. Tell kitchen fitter it is an aerial for your wireless bonding arrangement back to MET. He will definately believe you as he does not understand electrical type stuff thingys. Then tell customer it is free. Everyone will love you.

The main issue I have is this other "spark" being involved! Ideally I'd like the Gas to be bonded back to the MET but if he wasn't involved I'd quite happily have just noted on cert! If the units weren't removed I'd have never have known anyway as Clamp is present on incoming gas pipe and would have tested via a long lead!
 
Last edited by a moderator:
I know what to do here. Install a bonding clamp on gas pipe with a short piece of 1mm connected to it. Tell kitchen fitter it is an aerial for your wireless bonding arrangement back to MET. He will definately believe you as he does not understand electrical type stuff thingys. Then tell customer it is free. Everyone will love you.

It will only work with a green/yellow aerial though !;)
 
The main issue I have is this other "spark" being involved! Ideally I'd like the Gas to be bonded back to the MET but if he wasn't involved I'd quite happily have just noted on cert! If the units weren't removed I'd have never have known anyway as Clamp is present on incoming gas pipe and would have tested via a long lead!
Just to clarify, I was not serious about the RF bonding suggestion. (I want to patent it first before you lot start using it!)
 
Last edited:

Reply to Incoming Gas cross bonded off cold water in the Talk Electrician area at ElectriciansForums.net

Similar Threads

I like your way of thinking.
Replies
6
Views
462
loz2754
L
`Just wasted an hour doing the same, and came to the same conclusions. 600mm is only mentioned in respect of gas meters from the 14th on, and is...
Replies
21
Views
4K
  • Question
Actually I hadn't. I've taken on board everyone's comments, thank you.
2
Replies
26
Views
8K
  • Question
If it is unused it could be capped close to ground and covered with insulation at the main building. I.e. Opposite to first thought of bonding at...
2 3
Replies
52
Views
7K
  • Question
Why the thumbs down Bob; I was correcting myself ! Thanks for the concern anyway pal ?
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top