Doing a CU change in a flat, concrete floors and ceilings, just been decorated in hallways and bedrooms. Basically kitchen fitters ripped units out today and the bonding to the main gas has been cross bonded to the water behind units. Water is bonded back to the MET. However incoming water is bonded in a cupboard next to CU (nowhere near kitchen). There is absolutely no way I can get 10mm bonding back to the board without smashing hell out of the place!

Do I need to get this back to the MET or can I note on cert it's cross bonded! Absolute nightmate!
 
Can you join the gas bond to the water bond with a through crimp so it is one continous cable from the MET to both and it is unbroken?
 
It needs bonding either back to the MET, EMT if earthing conductor is adequate for bonding or joined on to the water bond either at the clamp or via a through crimp.
 
No, basically main water is bonded next to the front door - goes through a riser to each flat. The boiler (along with gas meter) is in the kitchen. 10mm bonding from gas pipe to the cold on the boiler.
 
If it's TNCS I'd say you have no choice but to bond the gas in 10mm back to the MET. TNS you might consider the current arrangement satisfactory assuming it tests OK,and write it as a departure. Your call on that,your name on the cert.
 
I would not be too concerned at all on this.Bear in mind, you did not install this bonding, so you are not initially verifiying it. You can only check / test it as you would an EICR.Use long lead test to confirm a sound connection between MET and the cold pipe you speak of. Ensure BS951 tags are present on earthing clamps. It is still effectively bonded just not exactly to what the non statutory document would like. Note on cert. No worries.
 
Problem is other spark/kitchen fitter is telling customer it needs to go back to CU! That's the problem here! I can't be bothered going back and forth with the other spark because ideally it should go back to CU! Customer wants me to do the work as she fears Kitchen fitters will over charge!
 
Problem is other spark/kitchen fitter is telling customer it needs to go back to CU! That's the problem here! I can't be bothered going back and forth with the other spark because ideally it should go back to CU! Customer wants me to do the work as she fears Kitchen fitters will over charge!

If she's willing to pay crack on...
 
Problem is other spark/kitchen fitter is telling customer it needs to go back to CU! That's the problem here! I can't be bothered going back and forth with the other spark because ideally it should go back to CU! Customer wants me to do the work as she fears Kitchen fitters will over charge!
Hell would freeze over before I ever took on board electrical advice from a kitchen fitter. Who is writing the cert, you or kitchen fitter?
 
I might be misreading the setup, but if the water bond is ok, then there is not a problem with through-crimping the existing bond and extending to the gas (as Leesparky has said)
 
I might be misreading the setup, but if the water bond is ok, then there is not a problem with through-crimping the existing bond and extending to the gas (as Leesparky has said)
It would not help him as he stated that the water bond is next to CU.
 

Reply to Incoming Gas cross bonded off cold water in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
276
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
780

Similar threads

I like your way of thinking.
Replies
6
Views
611
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top