Well then it can't be done then. Would not bother me at all. Note on cert. No worries.But doesn't want trunking or walls chased... Oh the joys!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Incoming Gas cross bonded off cold water in the Talk Electrician area at ElectriciansForums.net
Well then it can't be done then. Would not bother me at all. Note on cert. No worries.But doesn't want trunking or walls chased... Oh the joys!
It would not help him as he stated that the water bond is next to CU.
tel her she needs a magician not an electrician lolBut doesn't want trunking or walls chased... Oh the joys!
I know what to do here. Install a bonding clamp on gas pipe with a short piece of 1mm connected to it. Tell kitchen fitter it is an aerial for your wireless bonding arrangement back to MET. He will definately believe you as he does not understand electrical type stuff thingys. Then tell customer it is free. Everyone will love you.
I know what to do here. Install a bonding clamp on gas pipe with a short piece of 1mm connected to it. Tell kitchen fitter it is an aerial for your wireless bonding arrangement back to MET. He will definately believe you as he does not understand electrical type stuff thingys. Then tell customer it is free. Everyone will love you.
Of course, I feel a bit embarrassed now. How could it transmit an earth signal without it!It will only work with a green/yellow aerial though !
Just to clarify, I was not serious about the RF bonding suggestion. (I want to patent it first before you lot start using it!)The main issue I have is this other "spark" being involved! Ideally I'd like the Gas to be bonded back to the MET but if he wasn't involved I'd quite happily have just noted on cert! If the units weren't removed I'd have never have known anyway as Clamp is present on incoming gas pipe and would have tested via a long lead!
Of course, I feel a bit embarrassed now. How could it transmit an earth signal without it!
I dont have a regs book to hand so am working from memory here, but if it serves me correctly then:
If the cross sectional area of the copper of the water pipe is at least equal to the size required for a protective conductor (in this case a main bond) then it may be used as a protective conductor. But steps need to be taken to ensure that the pipe remains unbroken and electrical continuity be maintained if any alterations are carried out.
If we are talking about a loss of neutral (and therefore Earth on a TNCS system), most external gas supply pipes are plastic now anyway so isn't this a bit irrelevant?