Hi,

Can anyone suggest what advice they would give in the folllowing situation.

The incoming 240v armoured supply cable to a property runs under an area set out for a small extension - so the finished floor of the extension will cover the cable by some 18 inches and at that depth there will be a backfill of hardcore surrounding the cable. Is this acceptable or should the cable be run in conduit and if so what type ?

Thanks in anticipation.

Topcat
 
Should be installed in 50mm black flexible electric cable duct which you can get from some builder merchants and electrical wholesalers.

If is straight concentric cable and already connected you will need to cut the duct along its length to get the cable in.

If its lead i would speak to the DNO and ask what the best course of action would be as you really dont want to be pulling that around too much.
 
Last edited by a moderator:
Thanks jason.

It's a standard steel armour cable. Splitting the plastic cable duct so I could get the cable in as you suggest seemed the only way but I was a bit worried with the duct being surrounded by crusher run
which has to be well compacted and covered with 6 " of concrete !!

I wondered whether there may be some form of concrete ducting available with a top that could be fitted after the cable had been layed in.


Topcat
 

Reply to incoming mains supply under concrete in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
492
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top