Hi all,

I've just moved into a rented property and found the attached photo outside the conservatory. It spurs from an inside socket and goes down the garden to an outhouse. I've tried using the 18th edition to find some evidence that this is obviously the incorrect method, as I'd like to go to the agent with some good evidence.
There's also no RCD protection as the house has the old Wylex fuses.
Can anybody find something in the regs book that I could use? Is this even a pass on an electrical certificate?

Cheers all.

[ElectriciansForums.net] Incorrect SWA glanding/bonding
 
It is the Wylex WEM 80/2 100mA RCD (80A rated)
Thanks. As I said, that does not meet the (long required) need for outside sockets to be protected by a 30mA RCD. That should be provided on that garden SWA circuit too.
These days ALL circuits are required to have 30mA RCDs. The landlord may consider updating the whole fuse board. But regulations are not retrospective.

PS does your house have an earth rod somewhere outside with an earth wire connected to it?


I didn't think they were supposed to be enclosed in wood either, but could be wrong?
Whoever the muppet was that fitted the cupboard around the fuseboard did no think about the need to remove the front panel for maintenance!
A carpenter needs to remove sufficient wood to allow the front panel to be removed. No electrician will work on the installation without full access to the innerds!
Especially when/if landlord decides on an up to date consumer unit.
PS does the house have an earth rod somewhere outside with an earth wire connected to it?
 
Doesn’t BS951 specifically state those comps are for pipes?!
Hmm. Not just for pipes
[ElectriciansForums.net] Incorrect SWA glanding/bonding

“Other means of earthing” could include the armour of the SWA. So maybe it complies with BS951?
NO IT DOES NOT
Note 1 Specifically says that these clamps are not intended for the connection to the armour or sheath of a cable. !!!

probably contravenes 512-05-01 too.
 
Last edited:
A chap called Mark from the IET kindly provided me with this breakdown:


BS 7671:2018 requires that all equipment is suitable for the environment in which it is installed; the following regulation is explicit:

522.3.1 A wiring system shall be selected and erected so that no damage is caused by condensation or ingress of water during installation, use and maintenance. The completed wiring system shall comply with the IP degree of protection (see BS EN 60529) relevant to the particular location.
NOTE: Special considerations apply to wiring systems liable to frequent splashing, immersion or submersion.

The relevant IP rating is AD4 and IPX4:
As examples, the following special locations, i.e. similar outdoor environments exposed to the elements, have IPX4 requirements:

Caravan Parks:
708.512.1.1 Presence of water (AD)

Equipment shall be selected with a degree of protection of at least IPX4 in order to protect against water splashes (AD4).

Electric vehicle charging installations:
722.512.2.201 Presence of water (AD)

Where installed outdoors, the equipment shall be selected with a degree of protection of at least IPX4 in accordance with BS EN 60529 in order to protect against water splashes (AD4).

The BS 951 clamp around the cable is likely to damage it due to the pressure exerted:

522.8.1 A wiring system shall be selected and erected to avoid during installation, use or maintenance, damage to the sheath or insulation of cables and their terminations. The use of any lubricants that can have a detrimental effect on the cable or wiring system are not permitted.

Summary
  • The installation method in no way protects the cable and protective earthing connections from damage by exposure to water. Corrosion of the connections and armourings of the cable will occur very quickly in this type of situation. Loss of connection to the means of earthing is extremely dangerous and users of the connected equipment could be at risk of electric shock.
  • The steel-wire armoured (SWA) cable has been installed without the correct gland and shroud. Pressure exerted by the BS 951 clamp will, eventually, damage the cable’s insulation in this type of installation. Due to temperature, in summer the components expand, in winter the components contract. Failure of the insulation will mean that users of the connected equipment could be at risk of electric shock.
I hope this helps.
 
When I did my apprenticeship in the late 1990s you would never EVER have used an earth clamp on Swa cable like that in the picture... You would have been slung off site.
But in recent years I have noticed a heck of a lot of newly registered Sparks using earth clamps on Swa cables. Especially on park sites.
But imo its still rough as a badgers...
 
Using a 951 clamp like that runs the risk of damaging the insulation and the problems associated with having no insulation...
 

Reply to Incorrect SWA glanding/bonding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top