Basically customer currently only has a 100A 3 phase supply, which is rather overloaded. Also has a 120KVA generator for a 55KW motor.
Im trying to get a larger supply so everything will run off the grid and not overloaded.
Ive spoken to the DNO in terms of trying to get a 400A supply.
DNO has asked for a list of large motors, and starting method, which is:
15KW motor 3 phase - S/D
11KW motor 3 phase - Soft start
36KW motor 3 phase - Soft start
15KW motor 3 phase - S/D
15KW motor 3 phase - S/D
55KW motor 3 phase - Soft start
Total power before diversity is around 180KW
There is HV overhead lines onto customer property, with current 100KVA pole transformer.
Was hoping for just a transformer change, along with new overhead cable, then 400A panel board etc at my end.
However the DNO want to install a 500KVA ground mounted sub station at a cost of ÂŁ50,000.........
This seems rather excessive to me, and far more than the customer wants to spend...
The DNO are telling me its because of the starting current of the 36KW and 55KW motor.
They are using 164 starting amps for the 36, and 250A for the 55KW.
This doesn't sound right to me on a soft starter.
What do you guys think?
Im trying to get a larger supply so everything will run off the grid and not overloaded.
Ive spoken to the DNO in terms of trying to get a 400A supply.
DNO has asked for a list of large motors, and starting method, which is:
15KW motor 3 phase - S/D
11KW motor 3 phase - Soft start
36KW motor 3 phase - Soft start
15KW motor 3 phase - S/D
15KW motor 3 phase - S/D
55KW motor 3 phase - Soft start
Total power before diversity is around 180KW
There is HV overhead lines onto customer property, with current 100KVA pole transformer.
Was hoping for just a transformer change, along with new overhead cable, then 400A panel board etc at my end.
However the DNO want to install a 500KVA ground mounted sub station at a cost of ÂŁ50,000.........
This seems rather excessive to me, and far more than the customer wants to spend...
The DNO are telling me its because of the starting current of the 36KW and 55KW motor.
They are using 164 starting amps for the 36, and 250A for the 55KW.
This doesn't sound right to me on a soft starter.
What do you guys think?