Looking at a job where the customer has an indoor semi-raised swimming pool (large Jacuzzi half buried in the floor) & they want down lighters in the ceiling which will be about 2.1m from FFL.
The question is, do theses have to be SELV or can i get away with mains class 2 IP65.
Every time i read section 702 of the big blue book it seems to contradict the last regulation.
The SELV lights are not the problem, it's the locating of the transformers & the amount needed (35 down lighters on 5 circuits), according to the regs they are not allowed in Zone 1,2.
So the only place is the dist board cupboard which is 12m from the furthest down lighter.
.
The question is, do theses have to be SELV or can i get away with mains class 2 IP65.
Every time i read section 702 of the big blue book it seems to contradict the last regulation.
The SELV lights are not the problem, it's the locating of the transformers & the amount needed (35 down lighters on 5 circuits), according to the regs they are not allowed in Zone 1,2.
So the only place is the dist board cupboard which is 12m from the furthest down lighter.
.