Hi All, As part of one of my jobs for NIC accreditation I'm fitting an induction hob (8kw) and double oven (>2kw combined) the customer has requested they have separate switches on the same plate but does not want the oven on a socket should they change specification at a later date, any advice appreciated.
 
2 gang light switch feeding 40A contactors at the CU ;-)
how complex do you want go ?
:)

edit ; 40A contactor for the hob , 20A contactor for the double oven.
 
Last edited by a moderator:
So all-in-all if I can lead them away from the two switch idea I'd be better off advising one switch and running them through a dual appliance plate? Am I getting the gist?
 
I *think* that Click do a 45A DP switch as a 2G width module in their modular range, so you could get two switches side by side and even an FSU for something else all into one 6width enclosure on a double mounting box (need a 47mm one).

I know, as I've done it before, just can't quite remember what rating the switches are. 10mm to the first switch, then 4mm would do it jumping across to the second. Bit of a squeeze, but do-able.
 
I *think* that Click do a 45A DP switch as a 2G width module in their modular range, so you could get two switches side by side and even an FSU for something else all into one 6width enclosure on a double mounting box (need a 47mm one).

I know, as I've done it before, just can't quite remember what rating the switches are. 10mm to the first switch, then 4mm would do it jumping across to the second. Bit of a squeeze, but do-able.

Sorry - just checked - only go to 32A! If you wanted to play the diversity card carefully this might actually be OK for an 8kW load, though. It's a couple of amps under-rated at 230V.
 

Reply to Induction hob and oven switching in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
153
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
511
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
458

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
676
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
759

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top