I’ve been looking for the right answer and just can’t seem to find it.
I had an induction hob installed by a certified electrician, and there are no apparent problems so far, however, it is installed on the CU, RCD and upstream with a RCCB with no MCB,
I’m just not 100% sure if it’s the safest way to install it, I would personally think that would be safer on an RCBO or on a MCB, I’m not worried about overloading as it’s on a 10mm2 cable, 40a RCCB and the unit draws a max of 25Amp, I worry more about the fact that the RCCB will not protect on short circuit.
I appreciate any feedback or comments.
Thanks
 

Attachments

  • [ElectriciansForums.net] Induction hob correct install
    9683AA16-5980-4207-88CA-83C96C6EF8C1.jpeg
    557 KB · Views: 122
Would be interesting if @LastManOnline or @Risteard could chime in on this to clarify what is (and more importantly, what is not) acceptable in IE.

I can undersand the original installation being hurried, but can't see it having included three additional devices, from two other manufacturers.

Hopefully an REC can clear up what courses of action might be considered acceptable to remedy the situation.
 
Thanks, that's what I thought, then I came across this article, and made me very confused...
Proper RCCB connection Diagram with MCB. - https://www.etechnog.com/2018/12/rccb-connection-diagram.html

View attachment 83863
In that example the RCCB is not being protected from a short circuit from the load, the other way around the RCCB would not be protected from a short circuit of the cables between it and the energy meter, where is the most likely short circuit going to happen, opinions anyone? easiest solution is to install an RCBO.
 
Would be interesting if @LastManOnline or @Risteard could chime in on this to clarify what is (and more importantly, what is not) acceptable in IE.

I can undersand the original installation being hurried, but can't see it having included three additional devices, from two other manufacturers.

Hopefully an REC can clear up what courses of action might be considered acceptable to remedy the situation.
It is unusual for cooker circuits to have RCD protection in the south of Ireland. I would expect it to be fed from an MCB only, but certainly an RCBO or RCCB and MCB is allowable.

Not having overcurrent protection is, of course, completely prohibited.

Work on the distribution board cannot just be done by a qualified Electrician - they must be a Registered Electrical Contractor (REC), i.e. a member of RECI (aka Safe Electric). Can the OP confirm whether this was the case? If so, report it to RECI. If not, then it could be reported as illegal works.

A new circuit comes under Controlled Works No. 3 and requires a Completion Certificate. For an existing installation this will be a Completion Certificate for Existing Installations (Cert No. 3). A Cert No. 3 requires a Test Record Sheet to be supplied with it. (Other certs/reports do not currently, e.g. PIR, Cert No. 1 or Cert No. 2 - although with a PIR it's pretty much pushed by RECI that a TRS should be provided.)

A copy of Cert No. 3 and the accompanying TRS (or sheets plural with multiple DBs) is also required to be sent to RECI, so they should have a record of the works.
 
Last edited:
It is unusual for cooker circuits to have RCD protection in the south of Ireland. I would expect it to be fed from an MCB only, but certainly an RCBO or RCCB and MCB is allowable.

Not having overcurrent protection is, of course, completely prohibited.

Work on the distribution board cannot just be done by a qualified Electrician - they must be a Registered Electrical Contractor (REC), i.e. a member of RECI (aka Safe Electric). Can the OP confirm whether this was the case? If so, report it to RECI. If not, then it could be reported as illegal works.

A new circuit comes under Controlled Works No. 3 and requires a Completion Certificate. For an existing installation this will be a Completion Certificate for Existing Installations (Cert No. 3). A Cert No. 3 requires a Test Record Sheet to be supplied with it. (Other certs/reports do not currently, e.g. PIR, Cert No. 1 or Cert No. 2 - although with a PIR it's pretty much pushed by RECI that a TRS should be provided.)

A copy of Cert No. 3 and the accompanying TRS (or sheets plural with multiple DBs) is also required to be sent to RECI, so they should have a record of the works.
Thanks for your comments, to be honest at this point I'm not sure he was registered RECI or even qualified, he came with another bunch of cowboys that did our kitchen, and never provided any certs of completion or showered any RECI number what so ever, wanted little trouble and quick money, in and out! I guess three no surprise there... so the OP can't confirm any of the above, I will certainly contact RECI to check whether they have a record of the works and perhaps I can track the guy down to remedy this mess.

Thanks !
 
The likelihood of tracking down a non registered electrician is close to zero, I assume by your comments about the kitchen fitters (another bunch of cowboys) you have had cowboys work on your property before, whey did you go with them to install your kitchen.
 
I was going to ask if that is a Neozed fuse bottom-right which appears to feed a 63A MCB. And ideas why?
It's probably an old Diazed. There are newer Neozed switch fuses. It won't be feeding a 63A MCB but will be supplied through an isolator. The newer switch fuses disconnect the fuse when the latch is pulled down, and then the Neozed fuse can be pulled out or more usually screwed out.

It's because there has to be a main protective device on the customer's side of the installation to protect the DSO (ESB) fuse. It's a requirement of the Wiring Rules and of the ESB. Typically now there would be a 10kA MCB (technically only need to be 9kA, but these don't exist) in an IP rated enclosure in the bottom RHS of the Permalli Box.

A fuse can only now be used where this is within 3m of the ESB meter, so generally it will be an isolator in the DB with the Permalli Box setup as described above.
 
Thanks for your comments, to be honest at this point I'm not sure he was registered RECI or even qualified, he came with another bunch of cowboys that did our kitchen, and never provided any certs of completion or showered any RECI number what so ever, wanted little trouble and quick money, in and out! I guess three no surprise there... so the OP can't confirm any of the above, I will certainly contact RECI to check whether they have a record of the works and perhaps I can track the guy down to remedy this mess.

Thanks !
Your option is to report illegal works: Report Illegal Electrical Works - Contractors Area - https://safeelectric.ie/contractors/support/report-illegal-electrical-works/

Obviously it's your decision.
 

Reply to Induction hob correct install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
The OP is in New Zealand
Replies
3
Views
1K
davesparks
D
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
4K
Hi there, I'm facing the same issues with my Ikea Blixtsnabb (a rebranded Electrolux / AEG model) and wondering if I can achieve the same thing to...
Replies
9
Views
6K
  • Question
A socket-outlet could be connected to one of those circuits using 2.5mm² or as PC1966 says, even 1.5, although I personally would use 2.5 because...
Replies
6
Views
3K
  • Question
Hi I really cannot give you an answer if you need 2391 to do your own jobs, however I do know to get into an inspection council they ask for...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks