Induction hob on two phase. | on ElectriciansForums
Discuss Induction hob on two phase. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Mike Johnson
Nearly Esteemed
Wychling
Hi all
I have an induction hob that is wired up on two phase's of a three phase supply (oven on the third phase) the requirement for an isolation switch is giving me a bit of a headache as I can't seem to find a three pole domestic switch, any ideas?
Mike
Why a 3ph isolator at all?
Surely the diversity will bring it down to near 40A?
(And yes i am guessing BIG time on the rating :D)
It is a domestic kitchen in a French house which has a three phase supply, the beast in question is 8500 W, under French regulations the appliance must be able to be readily switched off, either from a wall switch or by being unplugged, so I am really looking for a solution that looks neat and unobtrusive.
Mike
Can't be tucked away, regulations say it must be readily available.
Lenny
Thanks for the link that looks like the best solution.
Mike
My Induction Hob, is roughly the same rating as yours, and mines been working fine on a 32A RCBO since i installed it...
If it's 2 phase and earth, (no neutral fo the hob) You can use a standard single or double box, DP cooker control switch!!!
What i'm saying is that you can use 2 of these standard single DP cooker switches in one of those boxes that allows 2X single face plates. So one switch can control the Hob, and the other the Oven. eg, two lines on one switch (hob) and line neutral on the other (oven)...
Two phase and earth, (No neutral for the hob)
How would that work on a Hob please explain I am keen to learn?
As I said on the original posts this is a two phase hob, the oven is on the other side of the room and requires its own isolator under the French Regulations, each phase is 20amp and the hob requires the two supplies to stop the main trip going out whith all four rings in operation, I am trying to ballance the load with the oven on the third phase.
Lenny has given me the best solution above.
Mike
Because phases are 3 separate wave forms.
If we took 3 generators and positioned them equidistantly 120 degree apart around a rotating magnet we would generate 3 completely separate ac waveform each with a phase displacement of 120 degrees of each other.
You therefore have a potential difference similar to the LINE-NEUTRAL of a single phase supply between the 2 phases. Here in the UK we have a 400/230 supply, often in continental Europe you will have 380/220 and in the US 208/127
So a lot of the American 208-230v volt Equipment will be of 2 phases.
Thanks for the reply.
I understand how an electric brushless motor works on the 120deg principle, but I don't see how an electrical element can work using two phase's of a three phase supply, (180 degs to each other) is there some tutorial I can go to that will explain it to me?
Mike
Mike
You can use as i already stated a normal Double Pole (DP) cooker switch that will fit a standard size flush back box or a standard white surface box for each, Hob and the Oven. It's not practical, or maybe not to French code to have a single isolator/switch controlling two cooking appliances that are distant from each other...
Try as you will, you won't ''balance'' the loads between a hob and and oven. What is the protective device in the CU/DB for this 3 phase supply?? Is it from one 3 or 4 pole breaker or 3 single pole breakers?? Are all the conductors in a single sheathed cable, or are they in singles in conduit??
I am not trying to isolate both from one isolator, I have two isolators, one each for the hob and oven, I want to isolate the two phase hob from one switch, the three phase's are controlled from the fuse box from a three combined 20amp (20amp/phase) cartridge breaker the wires are single sheathed in a conduit that runs to a three phase socket near the hob, I have plugged into this with the correct three phase plug and run this to an isolation switch on on to a cable outlet, thence onto the hob in heat proof 6mm cable, my problem prior to Lenny pointing it out was that I did not know there was a three pole switch available.
Now I just have to find a three pole cable outlet and 6mm four core cable.
Mike
Reply to Induction hob on two phase. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...