Engineer54
I am not trying to isolate both from one isolator, I have two isolators, one each for the hob and oven, I want to isolate the two phase hob from one switch, the three phase's are controlled from the fuse box from a three combined 20amp (20amp/phase) cartridge breaker the wires are single sheathed in a conduit that runs to a three phase socket near the hob, I have plugged into this with the correct three phase plug and run this to an isolation switch on on to a cable outlet, thence onto the hob in heat proof 6mm cable, my problem prior to Lenny pointing it out was that I did not know there was a three pole switch available.
Now I just have to find a three pole cable outlet and 6mm four core cable.
Mike
Ah, cartridge fuses, not exactly the best arrangement when protecting multi phase circuits....
So what your saying is, you have an isolation switch already for the oven, your just referring to the hob's means of isolation. So yes, a 3 pole switch would work, but then so would a DP switch, by making safe the unused phase (even removing fuse at th DB) and switching just the 2 phases at the DP switch. A DP switch is going to look far less industrial than a triple pole switch in the kitchen. Then you would only need a 2 pole socket outlet and 3 core cable. Do the French use a specific outlet and plug top for 2 phase +E ?? You may find that they do! It'll have to be a big-un to connect 6mm 3 core cable in the plug tops ....But it's your choice!! I really think it might be a good idea to have a talk with the local electrician!!
Personally, i would seriously think about getting your local electrician to upgrade your DB to a MCB distribution board too. At least then, if fault on one phase of a multi phase breaker appears the whole breaker trips not just one of the breakers, which is very bad news for any multi phase motors you may have.
Last edited by a moderator: