dazzlaaaaaa

hi everyone

first post, so please be gentle :)

Hoping someone can help me out. I have not been involved in very much installation work over the years as my job is more maintenance orientated. Work is currently installing a new industrial boiler and i am trying to work out cables schedules and fusing from distribution board to boiler panel. The boilers normal full load characteristics are 415v 34 amp full load. But the start up current is 134 amps approx. The main rise in start up current is caused by a force draft fan motor, wired in star/delta and a water feed pump. What i am pondering over is should I be sizing the cable and fuses accordingly to allow for start up current as I don't have any information on start up times and how long this start up current will be present for also these motors will be stopping and starting numerous times throughout the day.

Obviously dependent on whether i should be sizing for start up current will greatly affect size of cable I need to install.

Thanks everybody in advance

Hope someone can point me in the right direction
 
assuming a flc of 34A per phase, 6mm or 10mm, depending on derating factors and VD. the start-up current of 134A is for a very short duration and should be handled by either of those 2 conductor sizes. obviously type II or type III fuses will be required .
 
I believe that full load is 34a per phase not across all phases. I am definitely unable to use cb unfortunately as i know this would be ideal for inrush current, i am required to fuse the circuit within the old db that fed the removed boiler
 

Reply to Industrial Boiler Installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
333
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
985

Similar threads

D
  • Article
Issues With Nest Generation 3 Operating Boiler? I have a Google Nest Generation 3 Thermostat/Heatlink, Thermostat is in the hallway and operates...
Replies
0
Views
82
Dulbert
D
  • Question
Sorry for the late reply I found it very difficult to find work but I’m not sure if this was down to Covid and all the lock downs happening just...
Replies
2
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top