DNOs don’t like to supply PME to metal framed buildings with multiple users.
 
It’s part granite and part breeze block, Western Power planning department said the network didn’t support it and it wasn’t their job to provide a MET, see what the man says on Monday I suppose and I’ll report back
 
Well took a little longer to get here but seems we’re running a 35mm earth cable through the wall and expanding an earth block that was hidden away in the distribution room, seems weird even back in the 80s that they just put a 6mm earth cable from the consumer unit to the isolator but guess it must have been ok back in the day!
 
Back in the 80's having an earth in any size was a bonus given what I see from time to time. Spin is right though in terms of Western Power, they will not generally add a PME to a steel from. Normally they advise a TT.
 
Well took a little longer to get here but seems we’re running a 35mm earth cable through the wall and expanding an earth block that was hidden away in the distribution room, seems weird even back in the 80s that they just put a 6mm earth cable from the consumer unit to the isolator but guess it must have been ok back in the day!

Have you calculated the size of earth required?
 
I haven’t, the man in the know has, I thought he said 25mm before but he’s told me to get enough 35mm in to go through the wall into the meter cupboard where he’s connecting it in somewhere
 
I haven’t, the man in the know has, I thought he said 25mm before but he’s told me to get enough 35mm in to go through the wall into the meter cupboard where he’s connecting it in somewhere

What size is the incoming supply? You’ve shown a 100A cutout, but based on that you wouldn’t need anything bigger than a 16mm earth and actual calculation would probably prove the 6mm to be ok.
 

Reply to the thread, titled "Industrial Unit Earthing Arrangement - Lack of" which is posted in Commercial Electrical Advice on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top