So I've got my 2391... and was always taught and was under the impression that when carrying out R1+R2 tests on all circuits you must carry out the test at all points on the circuit, not the furthest point or a selection of points, I thought the test was to A. Prove a earth path that is suitable and B. Check polarity!

However one of the guys on the firm I work for yesterday has a grumble I was testing all points because it was 'taking too long' should I ignore him and carry on doing it my way or am I doing it wrong

Cheers
 
I would verify cpc continuity at all points. After all, the purpose of the test is to ensure that it is connected at all points and not just that there's a cpc path to the end of the circuit.

I would only conduct the Zs test at the end of the circuit though, having already proven continuity of the cpc.
 
When doing spot checks as QS I have observed that test results have been conducted at the last point of say a lighting circuit but as the permanent live in and out are at the switch then by testing only the last point of the circuit only confirms that the cpc is present at the last point.
I found that a light containing only a switch live and neutral did not have a cpc connected to the means of earthing as it had not been adequately connected at the switch point, so it’s important that it is done at all points.
This was a school job in which all lighting is metallic and as such ,exposed conductive parts.
 
Last edited:

Reply to Initial verification question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

  • Question
Recently did a job with new building techniques, at least to my experience. Dropped ceiling and metal studs in wals and ceiling. Insulation in...
Replies
3
Views
2K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top