And it is not just the landlords and letting agents looking at the quality of some of the EICR's

Corrected that for you

That will be a cloud based cert

Looking at most of the NICEIC and for that matter the NAPIT certs I have seen over the last few years the schemes don't add much if any credibility to the quality and accuracy of the reports their registered competent persons and approved contractors are producing
The schemes over the last 10 - 20 years have got themselves stuck in the money pit and are struggling to climb out of it to re-establish a standard that they had in the past before the race to the bottom that was driven by Emma Clancy when she was at the helm of certsure
I like your view!! These compaies are not adding any value to the profession. To me a qualified person who has worked hard and passed his exams successfully does not need need a watch dog who charges 1000s a year just to allow them do their job. Thi country has ha it. Sorry. I agree there must be CPD requirement et. but not by private money making corps
 
I've seen good and bad reports by cps and non cps sparks. You need to be confident you are competent to carry them out, imo that would still mean you carry 2391 or equivalent.

Being non cps does mean you won't always be able to actually correct the non compliances you identify yourself though, domestically of course, if board changes etc are required or other things lead to notifiable works then you have the potentially embarrassing conversation of, "this is wrong but im not allowed to fix it". Thus providing only half of the full service really, you'd need to inform your clients of this fact prior to getting the job imo.
 
I've seen good and bad reports by cps and non cps sparks. You need to be confident you are competent to carry them out, imo that would still mean you carry 2391 or equivalent.

Being non cps does mean you won't always be able to actually correct the non compliances you identify yourself though, domestically of course, if board changes etc are required or other things lead to notifiable works then you have the potentially embarrassing conversation of, "this is wrong but im not allowed to fix it". Thus providing only half of the full service really, you'd need to inform your clients of this fact prior to getting the job imo.

The service under discussion is the compilation and provision of a report, after inspection and testing of an installation. Nothing more and nothing less should be considered 'the full service'.

Anything other than the above should be agreed by both parties prior to work commencing.
 
The service under discussion is the compilation and provision of a report, after inspection and testing of an installation. Nothing more and nothing less should be considered 'the full service'.

Anything other than the above should be agreed by both parties prior to work commencing.
I take my van for an mot fully expecting the garage to be able to fix any identified problems, i wouldn't consider a company that could identify problems and do nothing about them.

This should be considered if thats his buisness model, testing only, that potentially the attractiveness of his service is then less so to prospective customers. They could look for others that can find and fix.
 
I take my van for an mot fully expecting the garage to be able to fix any identified problems, i wouldn't consider a company that could identify problems and do nothing about them.

This should be considered if thats his buisness model, testing only, that potentially the attractiveness of his service is then less so to prospective customers. They could look for others that can find and fix.
Depending on the client and explaining the situation.

I think most sparks would do the work and get a matey to sign it off or just give the report.
 
I take my van for an mot fully expecting the garage to be able to fix any identified problems, i wouldn't consider a company that could identify problems and do nothing about them.

This should be considered if thats his buisness model, testing only, that potentially the attractiveness of his service is then less so to prospective customers. They could look for others that can find and fix.

In NI we take our vehicles to a government test centre and it passes or fails - if work is required then we have that carried out at a garage and make an appointment to have it re-tested.

There is no conflict of interest and no possibility that a test centre will be touting for business.

Regardless of whatever merits your analogy may or may not possess, when an electrician is contracted to carry out an EICR they are being asked to inspect, test and report. Anything beyond that falls outside of the scope of an EICR. Whether or not an electrician wishes to agree additional works up front or quote for remedial works is a separate matter.
 
Looking at most of the NICEIC and for that matter the NAPIT certs I have seen over the last few years the schemes don't add much if any credibility to the quality and accuracy of the reports their registered competent persons and approved contractors are producing
The schemes over the last 10 - 20 years have got themselves stuck in the money pit and are struggling to climb out of it to re-establish a standard that they had in the past before the race to the bottom that was driven by Emma Clancy when she was at the helm of certsure
I wouldn't care to defend the schemes and yes a lot of dross finds it's way past their checks and onto their paperwork, but like it or not they are the industries compliance mechanism so working around them just seems a faff and self restricting and would make people question you.

I don't wholly buy the "oh you can still do industrial innit", if a few more managers etc understood their obligations in law, and what they could potentially be deemed culpable of when they employed dodgy Joe down the road to carry out electrical work they'd also be far keener to use someone who can be fingered should the fit hit the shan.
 
I take my van for an mot fully expecting the garage to be able to fix any identified problems, i wouldn't consider a company that could identify problems and do nothing about them.
I certainly have a different view my father was a mechanic and my 2 brothers are recently retired mechanics and they would never go to a garage for an MOT that does repairs as they are quite often looking for work rather than carrying out an honest MOT. The MOT test garage all the family and quite a number of friends currently use and have done for the last 15 or more years does a fair and genuine MOT the fact they don't do repairs does in no way affect what they do it keeps 2 MOT testers busy all day everyday 5 days a week and every other Saturday morning
The big problem these days most vehicles now require expensive specialist tooling and diagnostics so some MOT centres may not be equiped due to the costs involved to repair all vehicles
This should be considered if thats his buisness model, testing only, that potentially the attractiveness of his service is then less so to prospective customers. They could look for others that can find and fix.
I don't see any reason why someone who is semi retired couldn't just do test & inspection with maybe some very minor remedial work without all the hassle of doing the more major remedial work
 
I wouldn't care to defend the schemes and yes a lot of dross finds it's way past their checks and onto their paperwork,
Your statement seems at odds with your posts that appear to be pro scheme
but like it or not they are the industries compliance mechanism
That is where you are being misled try making a complaint then you will find out that they are far from it
so working around them just seems a faff and self restricting and would make people question you.
The schemes have been misleading people for years aided and abetted by the media
I don't wholly buy the "oh you can still do industrial innit", if a few more managers etc understood their obligations in law, and what they could potentially be deemed culpable of when they employed dodgy Joe down the road to carry out electrical work they'd also be far keener to use someone who can be fingered should the fit hit the shan.
A lot of it comes down to how a Dutyholder discharges their Duty of care, but the question then is how to carry out due diligence on a contractor before placing the order do you accept the NICEIC / NAPIT model where it is assumed that they have done it on your behalf and what will be delivered is an honest and genuine report which truly reflects the condition of the installation the issue then is can the dutyholder easily validate what is in the report to ensure they have met their duty of care

The part I have never understood is how NICEIC and NAPIT validate a contractors ability and skillset to carry out EICR's when they don't appear to have any assessment procedure for doing so
 
The semi retired referred to above is much more likely to have the experience to accurately assess the age of an existing installation to determine which things that would now be C2 can be marked as C3.
Hopefully that was the point I was making as experience IMO is a big factor when carrying out EICR's
 
I've seen good and bad reports by cps and non cps sparks. You need to be confident you are competent to carry them out, imo that would still mean you carry 2391 or equivalent.

Being non cps does mean you won't always be able to actually correct the non compliances you identify yourself though, domestically of course, if board changes etc are required or other things lead to notifiable works then you have the potentially embarrassing conversation of, "this is wrong but im not allowed to fix it". Thus providing only half of the full service really, you'd need to inform your clients of

I wouldn't care to defend the schemes and yes a lot of dross finds it's way past their checks and onto their paperwork, but like it or not they are the industries compliance mechanism so working around them just seems a faff and self restricting and would make people question you.

I don't wholly buy the "oh you can still do industrial innit", if a few more managers etc understood their obligations in law, and what they could potentially be deemed culpable of when they employed dodgy Joe down the road to carry out electrical work they'd also be far keener to use someone who can be fingered should the fit hit the shan.

I certainly have a different view my father was a mechanic and my 2 brothers are recently retired mechanics and they would never go to a garage for an MOT that does repairs as they are quite often looking for work rather than carrying out an honest MOT. The MOT test garage all the family and quite a number of friends currently use and have done for the last 15 or more years does a fair and genuine MOT the fact they don't do repairs does in no way affect what they do it keeps 2 MOT testers busy all day everyday 5 days a week and every other Saturday morning
The big problem these days most vehicles now require expensive specialist tooling and diagnostics so some MOT centres may not be equiped due to the costs involved to repair all vehicles

I don't see any reason why someone who is semi retired couldn't just do test & inspection with maybe some very minor remedial work without all the hassle of doing the more major remedial work
Thanks UNG, that is exactly the point. I am 61 now and I am already planning to do test an inspection when I retire in 3 years' time. I am doing my 2391-52 course in a few weeks' time to refresh my knowledge, just to be on the safe side! I will start already now doing this for some friends (I have 5 that need this service). It will be some good exercise as well. With regards to e.g. change of consumer unit, if required, I could contact the Building Authorities and get permission (perhaps to start with as I am doing this for friends).
My Degrees: MSc, MBA - Additioanl IEng MIET from 2005.
My old qualifications:
NVQ L 4 , Denmark (Domestic, Commercial and Industrial), 20 years experience (10 year Automation).
UK , 17th and 18th Edition, and Part P
Now doing 2391-52

So I hope I will be good enough for the purpose :)
 
Probably more about setting a bar, but lay people have little understanding of what it means to be registered with a scheme.
A position carefully cultivated by the scams with their "use our members if you value your life and the lives of your children" style of messaging.

I take my van for an mot fully expecting the garage to be able to fix any identified problems, i wouldn't consider a company that could identify problems and do nothing about them.
Alternatively, as already pointed out, you can be reasonably sure they aren't treating MOTs as work generators for the workshop. In the past I've taken my motors (esp. Land Rovers) for an MOT fully expecting to do any work myself.
 
A lot of it comes down to how a Dutyholder discharges their Duty of care, but the question then is how to carry out due diligence on a contractor before placing the order do you accept the NICEIC / NAPIT model where it is assumed that they have done it on your behalf ...
Indeed, and given that (in my experience) agents know nothing about electrickery, it's the only way they can do that. When the routine inspaction rule came in, I got an email from the agent which copied verbatin what they'd got from NICEIC. I ripped it to shreds as it had (from memory) 5 false statements in just 2 sentences ! I don't think they like me very much - but when I have to point out basic errors like that, there's some mutuality there !
 
Your statement seems at odds with your posts that appear to be pro scheme

That is where you are being misled try making a complaint then you will find out that they are far from it

The schemes have been misleading people for years aided and abetted by the media

A lot of it comes down to how a Dutyholder discharges their Duty of care, but the question then is how to carry out due diligence on a contractor before placing the order do you accept the NICEIC / NAPIT model where it is assumed that they have done it on your behalf and what will be delivered is an honest and genuine report which truly reflects the condition of the installation the issue then is can the dutyholder easily validate what is in the report to ensure they have met their duty of care

The part I have never understood is how NICEIC and NAPIT validate a contractors ability and skillset to carry out EICR's when they don't appear to have any assessment procedure for doing so
I'm not sure I've said anything especially pro scheme? I think they're quite flawed and have said such, feel free to highlight anything that contradicts that.

But they are the structure that's in place and I think working around them doesn't make business sense. Only yesterday I was having a conversation with a business owner over his obligations to his employees, that while part P doesn't apply to businesses as (like in purchase protection) business is considered professional purchasers, that doesn't mean they can employ anyone and still have due diligence..

While any bandit can get away with overpricing I think being scheme allows you to justify higher prices.

A lot of shoddy drivers have a licence but would you get in a cab of someone who didn't?
 

Reply to Inspection&Test and EICR in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
181
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
556
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

  • Question
This isn't at all unusual. Companies often use subbies and as such are just essentially paying for their services resulting in little or no...
Replies
7
Views
850
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
692

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top