Hi All. Just a little help I need connecting a electric oven and induction hob. The existing is a 32 amp MCB in the consumer unit. A 4m run of 6mm sq t&e cable from mcb going to a 45A cooker control switch. From here a 6mm sq t&e going into cooker connection unit. I have removed the old electric oven which was connected to the cooker connection unit with 6mm sq t&e cable. I want to connect a new 2.5kw oven and a 6.4kw induction hob. I have a 45 Amp Dual Appliance / Cooker Outlet Plate which will replace the existing cooker connection unit. Is it ok to connect both appliances to the new dual appliance connection unit so they are on the same circuit. If so then what size cable do I need to connect the oven to the connection unit. The hob already has a 5 core cable with the blue and grey cable joined together at the end and the black and brown also joined together. It looks like a 3 phase cable. Any help on this will be much appreciated.
Thanx
 
same electrickery these days in spite of the EU(rinal) woth their stupid cable colours and phantom 230V.

Neither of those were anything to do with the EU, but I take your point.

So I can do it even though the instructions say "This appliance must be connected directly to the mains using an omnipolar circuit breaker with a minimum opening of 3mm between contacts"

Indeed, the instructions are guidance not law.
 
ovens and hobs up to a total rating of 15kW have been fine for the last 60 + years with both on a 32A MCB (6.0mm cable, ref. method withstanding). same loads, same electrickery these days in spite of the EU(rinal) woth their stupid cable colours and phantom 230V. why should it change?
Is this your personal rule of thumb? Based on I guess a circa 50% diversity factor for the 6mm/B32 combo?
 
it's a well used formula... 10A + 30% of remainder
Just had a look at OSG (amd3, havent got latest to hand) and you are correct for assessment of load on a final circuit to use that formula, can't get 15kW though...I get 13.8 to 14.4 depending on which voltage you prefer (!) thats for 2 appliances on same circuit.
 

Reply to Install new oven & induction hob to existing circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
581
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
767
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
519
I believe the 6mm and 40A MCB debate is a little contentious at times. It depends on the installation method, being pretty close to the tabulated...
Replies
3
Views
597

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top