If a install is not provided with a main isolator who should out one in?
Old install, no main switch, just the fuse then meter
Should i install one for the customer or should it be to request the DNO to install after the meter? The tails from the meter are more than 3mts long so it needs to be done if i have interpreted the regs correct?
 
Meter tails longer than 3m should now be provided with a protective fusing however unless you are changing anything to do with the tails I would tend to leave as is.
If you were installing them for the first time then fusing should be supplied.

An isolator is a different matter, it is very much easier for us if there is an isolator between meter and board, though frequently there is not one present and there are no regulations to require this.
Since this would require the removal of the DNO fuse then as Paulm says worth checking with the DNO for a price as they can then do the whole job as one.

You can fit one yourself but still need the fuse removed.
 
Meter tails longer than 3m should now be provided with a protective fusing however unless you are changing anything to do with the tails I would tend to leave as is.
If you were installing them for the first time then fusing should be supplied.

This thorny old issue!
According to NIC you don't need additional fusing for tails over 3 meters only isolation, assuming correct ccc of tails etc.
I have spoken to Western Power about it, they don't require it so it doesn't appear to be a DNO requirement.
Having spoken to British Gas about it they don't require it either. Also I don't think it's in th BGB, although there is a reg 433.?.? (might not be right) but it refers to reduced ccc cables requiring fusing within 3 meters of the ccc reduction.

Duck and indeed cover.
 
This thorny old issue!
According to NIC you don't need additional fusing for tails over 3 meters only isolation, assuming correct ccc of tails etc.
I have spoken to Western Power about it, they don't require it so it doesn't appear to be a DNO requirement.
Having spoken to British Gas about it they don't require it either. Also I don't think it's in th BGB, although there is a reg 433.?.? (might not be right) but it refers to reduced ccc cables requiring fusing within 3 meters of the ccc reduction.

Duck and indeed cover.

That is interesting because there is every chance that you could argue the 3 metre rule on the basis of type of cable/conductor as the supply cable coming in would not be double sheathed tails but most likely a multi-sheathed cable.

It would be interesting to know what the DNO thinking is on this, most likely it will be due to the RCD protection now being afforded in most domestic situations
 
That is interesting because there is every chance that you could argue the 3 metre rule on the basis of type of cable/conductor as the supply cable coming in would not be double sheathed tails but most likely a multi-sheathed cable.

It would be interesting to know what the DNO thinking is on this, most likely it will be due to the RCD protection now being afforded in most domestic situations

The bloke I spoke to at Western Power didn't know anything about our regs mentioning the DNO and their "requirements" re length of tails.
He was with the engineering department, so not just a numpty.
As I've already said, he did say they would require additional isolation but wasn't concerned with additional fusing for tails over 3 meters. I'll point out that the tails in question are 25mm so the DNO fuse of 100 amps will protect them perfectly well IMHO.
 
The bloke I spoke to at Western Power didn't know anything about our regs mentioning the DNO and their "requirements" re length of tails.
He was with the engineering department, so not just a numpty.
As I've already said, he did say they would require additional isolation but wasn't concerned with additional fusing for tails over 3 meters. I'll point out that the tails in question are 25mm so the DNO fuse of 100 amps will protect them perfectly well IMHO.

If your DNO agrees (and probably you have it in writing) then there is no problem as the regs state "unless the supplier agrees" that their protection is OK.
Generally it is going to be easier to change your fuse (legally) than the supply fuse so hope yours goes first.
Isolation would be required as close as practicable and the change in cabling type may well require a fuse according to BS7671 unless agreed with the supplier.

I must admit I have not read any of the DNO's "electricians information" section for fusing down, I must try sometime.
 
Last edited:

Reply to Installation main switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
282
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
792

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
485
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
785

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top