Are you installing a charger or just a socket to feed a charger?
The RCD requirement is a different type to the usual RCD so even if there is already RCD protection you'll probably need to provide additional protection
yes 722.531.2.101
That could be interesting to accomplish if the CU is a dual RCD board. 722.531.2.101 states protected 'individually' by an RCD! You could easily add another RCD to protect just that point (to meet the reg) but then theres no discrimination so it would be pointless.
I have always fitted a charger with the correct outlet for a car, I'm not aware of an option that would allow you to connect a car to a 32A commando socket, it doesn't seem right.
all EV cars as far as I am aware have a type 1 or type 2 inlet and you need a suitable lead, and non or them go to a commando socket, I would 100% clarify exactly what it is is being plugged in.
Just to add, if it was just on a normal commando socket, it would allow you to just pull it out without turning it off which is why you use the correct lead
If the customer has asked you to install a 32A commando socket then that is what you do really.
If the customer then decides to plug in an electric car to that socket that is up to him, you cannot dictate what the use to which a socket may be put. To meet the charging safety requirements the charger being used should be independently adequately protected.
If the car were charging on a BS1363 socket it could also be a general use socket.
However if you do have a TT system then this does simplify the install even if you do take account of the charging point requirements it is only the type A / B RCD protection that causes hassle, but most car charging units have these fitted anyway.
Does the current guidance still have the domestic "we know what is going to happen" exclusion for TNCS systems?
Yes 722.411.4.1 I believe is still current so practicality can take over if the supply is TNCS (PME).
(Now that I have looked it up, I really ought to read the current regs!)