Hi all,

I was testing a property yesterday, and had a a very low resistance between neutral and cpc, it was 0.39Mohms, between live and earth = 500Mohms and live and neutral 398Mohms. Iv unplugged everything and took all sockets down to see if n and cpc was touching but could not see anything. Could someone please let me know what could cause and how to find the fault?

Regards

jim
 
split the circuit and track the low reading down, splitting again and again till you locate it. a good idea is to disconnect anything that goes outside first and ensure there's nothing plugged into hidden sockets/FCUs. BTW< is it a socket cicuit/lighting circuit/ other?
 
Hi all,

I was testing a property yesterday, and had a a very low resistance between neutral and cpc, it was 0.39Mohms, between live and earth = 500Mohms and live and neutral 398Mohms. Iv unplugged everything and took all sockets down to see if n and cpc was touching but could not see anything. Could someone please let me know what could cause and how to find the fault?

Regards

jim

Good luck Jim! Lucky you didn't find this after a CU change :grin:.

This is something I need alot of practise on too!! I had a 0 MΩ N-E and split the ring and eventually after 3 hrs found a box screw just slightly bitten inro the neutral!! The point is I dont think you would have a reading of any ohms if they were actually touching, a part from that I cant be of any more help. I also dont see how it could be anything plugged in if your L-N is ok!!
 
Tel, you are not helping. For this forum to help people we need them to offer up their ideas first.

If we just charge in with answers people won't learn to think for themselves.

well, my comment was only a logical suggestion. he'll still need to use his head to locate the problem.
 
Could I just plug the plug in lead in to every socket intill I get 0Mohms, as there is a load of junk everywhere, bed in the way and all the stuff from the loft in rooms. Iv taken most of the sockets down i could physically get too. Would this help me find the the fault or not?

Cheers
 
Could I just plug the plug in lead in to every socket intill I get 0Mohms, as there is a load of junk everywhere, bed in the way and all the stuff from the loft in rooms. Iv taken most of the sockets down i could physically get too. Would this help me find the the fault or not?

Cheers

why would you expect to get a reading of 0 ohms? think a bit.
 
Could I just plug the plug in lead in to every socket intill I get 0Mohms, as there is a load of junk everywhere, bed in the way and all the stuff from the loft in rooms. Iv taken most of the sockets down i could physically get too. Would this help me find the the fault or not?

Cheers

I thought you said you'd unplugged EVERYTHING. Clearly you may not have.

First rule - retrace ring and make sure everything IS unplugged.
 
Follow Tel's advice in post 3 with your IR tester, best to test at 250v if you're not sure if you have disconnected everything. I'm surprised that you are 4th year apprentice and haven't done any fault finding.
 
Last edited by a moderator:
^^^^^ shut up , if your not going to help the guy then don't comment , hes being honest and learning as he goes

Don't tell me to shut up! This is what's wrong with the trade now. People like you think that it's ok to tackle jobs without any training or experience at all, just because the person is "being honest".
 
^^^^^ shut up , if your not going to help the guy then don't comment , hes being honest and learning as he goes

I'm thinking of becoming gas safe registered so can I come and work on your boiler (I don't want to work on mine in case I break it) I'll charge you for the inconvenience as well ;)
 
I am interested in this thread as i don't have a lot of experience in testing either , i dont want to read thru pages and pages of people telling the guy he needs this and that and he shouldnt be doing it , am sure hes heard it all before on here , if u want to write all that crap start your own thread about it , otherwise read his first post and answer the question
 
Whatever next! specialist fault finding teams to bail out all the "sparks"who don't know how to fault find?
fault finding is a basic part of electrical work that has to be taught .you don't get it in a book or on the Internet.
it takes years to get proficient in quick fault diagnosis IMO.
Learning on the hoof and tring to blag your way out of it is not gonna happen.
some of the threads on here recently really boil my Pish with the complete lack of knowledge of even the basics
and then getting huffy when they get found out for the roasters that they are.
 
question has been answered . advice has been posted. other than going there to do the job--- he has to put in the effort himself.
 

Reply to Installation resistance of 0.39Mohms n -e in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
Replies
24
Views
3K
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
489
loz2754
L
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
Recommend this: Electricians Guide to Inspection and Testing Book -...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks