New here so sorry if posted in wrong place,
I have installed a new consumer unit as the title says it’s a split load rcd board, anyway to the point one of the rings seems to now have a neutral fault which is taking out one side of the board I have checked all obvious things, touched no appliances since installing only moved the existing wiring to the new board location etc. The thing that I can’t get my head round is I have continuity end to end but on both legs of the ring I have a short between live and neutral, all I can think of now is to IRT the circuit and see maybe this could be down the the install being 30 years old and degraded T&E over time? Maybe the inner cores are now touching? Seems funny tho because the old c/u was old but was still rcd protected so surely that would of seen the fault? And surely both legs wouldn’t have sustained damaged when I’ve moved the cables?
can give me details if required thanks in advance
 
30 years is nothing for decent PVC wire that has not been abused (thermally or physically).

As above, did you do an IR test before all the circuits were re-connected and put in to use?

L-N or L-E faults are pretty obvious no matter what the old CU was, but N-E could have been there for years and without an RCD nobody would have notice.
 
As Tel says, more precise measurements, rather than a "short" which is somewhat vague and not very helpful.

For example, if a fraction of an Ohm N to E, then it is often easy to track down where in the wiring this is.

Also, do you have measurements for all the other circuits on this RCD that is tripping? E.g. a N to E short on a circuit that didn't used to have RCD protection, on this RCD, now causing the socket circuit to trip when under load.

I'm sort of assuming you do have an MFT and did make some measurements?
 
Last edited:
did you not do a EICR before hand .
Don’t need to do an EICR beforehand, what difference would that make? When upgrading the consumer unit you have to do an install certificate anyway, Going back to the OP you need to use your tester to find the fault now, Split the ring at board then guess mid point one side should be clear with high readings the other 0 by swnds of it. Chase the fault is pretty much really easy when you understand the logic
 
The reason we do an EICR before hand, or at the very least a site survey with some testing as the minimum, (as recommended I’m the best practice guide), is to find and iron out any problems prior to fitting a new board.

You should also be carrying out a full range of tests before energising the board and not just doing the bang test to bring it into service.
 
Re-reading the OP's post it does sound like that act of moving the cables over has triggered a fault.

However, before it was all live I would have expected the usual test to have shown this up (IR, ring continuity, R2 or R1+R2 for lights, etc, etc).

Irrespective of how they got here, the next step for the OP is to do fault-finding to identify what the issue is. So take the final circuits out and IR test them (loads off/unplugged) and when the offending circuit is identified, then do the usual process to locate the fault (e.g. split half-way and see if it is a fault in the 1st or 2nd half, rinse and repeat...)
 
The reason we do an EICR before hand, or at the very least a site survey with some testing as the minimum, (as recommended I’m the best practice guide), is to find and iron out any problems prior to fitting a new board.

You should also be carrying out a full range of tests before energising the board and not just doing the bang test to bring it into service.
I’m guessing you charge for full EICR prior to advising a board change? I’ll do a pre survey of standard things like main earth, bonding, condition of accessories (age) advise customer that should any faults be found whilst testing then additional cost involved. Also you test it after completing consumer unite has been changed and this particular issue would have been picked up if done properly.
 
an eicr would have detected this fault before you changed the consumer unit.
This fault would have been picked up after board change. Carrying out the correct testing schedule. Simple stuff this don’t need to be charging for an EICR and then charging for board change, change the board rectify any faults and all sorted.
 
Hi - I’m assuming that one RCD is now tripping? Are the circuits in the new board on the correct N bar? If you post a pic it can often be seen if there’s a simple wiring error of that sort.
 

Reply to Installed a new C/U now have fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
489

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top