New here so sorry if posted in wrong place,
I have installed a new consumer unit as the title says it’s a split load rcd board, anyway to the point one of the rings seems to now have a neutral fault which is taking out one side of the board I have checked all obvious things, touched no appliances since installing only moved the existing wiring to the new board location etc. The thing that I can’t get my head round is I have continuity end to end but on both legs of the ring I have a short between live and neutral, all I can think of now is to IRT the circuit and see maybe this could be down the the install being 30 years old and degraded T&E over time? Maybe the inner cores are now touching? Seems funny tho because the old c/u was old but was still rcd protected so surely that would of seen the fault? And surely both legs wouldn’t have sustained damaged when I’ve moved the cables?
can give me details if required thanks in advance
Don’t need to do an EICR beforehand, what difference would that make? When upgrading the consumer unit you have to do an install certificate anyway, Going back to the OP you need to use your tester to find the fault now, Split the ring at board then guess mid point one side should be clear with high readings the other 0 by swnds of it. Chase the fault is pretty much really easy when you understand the logic
Have had 2 x dislikes for this post, if you can explain you’re dislike that would be beneficial. I’m open for debate rather than a ?
i would not do a full EICR preceding a CU change, but would conduct sufficient tests to save a fault/s biting me in the arse. if the old CU has an upfront RCD that tests as OK , half the battle is won already.
I suspect the OP only hid their profile after realising we knew he/she had been viewing this thread numerous times but had not responded (shortly after DPG's post #31)....
The profile was hidden early on long before post #31, I generally look at the OP and look at the profile of the OP before commenting and I lurked for a while on this one before making my comment
Yes is frustrating when people post on here with situations like the OP and then don’t give us the outcome or update, I understand if their busy then not always possible to reply straight away but at least reply. Anyhow if it was genuine hope he found the fault
Reply to Installed a new C/U now have fault in the UK Electrical Forum area at ElectriciansForums.net
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...