Morning all. I’m getting to be a regular poster on here (it is an awesome source of info, thank you all). So, discussing with a seasoned electrician this week (I’m a relative newbie to the trade). So 4mm cable run as a radial on a 32A mcb, now reference method 100 states max current is 27A. They are saying it’s ok but I’m not sure regarding when it gets documented for a EIC; would this not get picked up by the governing body as not meeting the regs. Or am I being to ‘by the book’ as my view is it should be down rated to a 25A mcb. If it went ahead as the 32A mcb would it be ok to be documented on EIC as reference method 100 even though it’s a higher A rating than the OSG states. Some guidance would be truly helpful.