The resistance of the installation electrode should be as low as practicable a value of exceeding 200 ohms may not be stableIt is the neutral to earth link, it is the link which references the neutral to the general mass of earth.
And yes it is not a TT system, it is a TNS system which you are creating.
200ohm is not the value we would use on a TT arrangement, that is a misinterpreted suggestion from the regulations on what may be a limit of stability in some situations.
Table 41.5 note 2 bs7671.
200ohms is the adopted figure used I would say!
If you want to be percise it is RA x Idelta N equal to or less than 50v which I'm sure you know this.
If I'm incorrect about the earth neutral link then hey I stand corrected