It is the neutral to earth link, it is the link which references the neutral to the general mass of earth.
And yes it is not a TT system, it is a TNS system which you are creating.

200ohm is not the value we would use on a TT arrangement, that is a misinterpreted suggestion from the regulations on what may be a limit of stability in some situations.
The resistance of the installation electrode should be as low as practicable a value of exceeding 200 ohms may not be stable
Table 41.5 note 2 bs7671.
200ohms is the adopted figure used I would say!
If you want to be percise it is RA x Idelta N equal to or less than 50v which I'm sure you know this.
If I'm incorrect about the earth neutral link then hey I stand corrected
 
The resistance of the installation electrode should be as low as practicable a value of exceeding 200 ohms may not be stable
Table 41.5 note 2 bs7671.
200ohms is the adopted figure used I would say!
If you want to be percise it is RA x Idelta N equal to or less than 50v which I'm sure you know this.
If I'm incorrect about the earth neutral link then hey I stand corrected
When using an rcd for fault protection purposes
 
The resistance of the installation electrode should be as low as practicable a value of exceeding 200 ohms may not be stable
Table 41.5 note 2 bs7671.
200ohms is the adopted figure used I would say!
If you want to be percise it is RA x Idelta N equal to or less than 50v which I'm sure you know this.
If I'm incorrect about the earth neutral link then hey I stand corrected

'May not be stable' that does not mean that it is a suggested value, maximum value or even that a value less than it is stable.
'As low as practicable' does not mean that you are aiming for a particular value, it means getting it as low as you practically can, which in most cases is a lot less than 200 ohms.

I do know about that calculation, but there are more factors to consider, for example if you read the instructions for a Schneider rcbo they state a maximum Zs for the protected circuit of 100ohms.

the generator as supplied will have a link which connects the star point of the alternator to the case of the generator, this is not a neutral to earth link as there is no connection to earth and it for small an IT supply. By connecting the star point to the general mass of earth it can be turned in to a TNS supply.
 
'May not be stable' that does not mean that it is a suggested value, maximum value or even that a value less than it is stable.
'As low as practicable' does not mean that you are aiming for a particular value, it means getting it as low as you practically can, which in most cases is a lot less than 200 ohms.

I do know about that calculation, but there are more factors to consider, for example if you read the instructions for a Schneider rcbo they state a maximum Zs for the protected circuit of 100ohms.

the generator as supplied will have a link which connects the star point of the alternator to the case of the generator, this is not a neutral to earth link as there is no connection to earth and it for small an IT supply. By connecting the star point to the general mass of earth it can be turned in to a TNS supply.
The 'calculation ' is from bs 7671 RA sum of resistance of electrode and associated cpc stating that the total resistance x by say a 30mA rcd cannot be greater than the recommended 50v touch voltage.
Ideally get the electrode as low as possible i never said there was a magic number to aim for other than what is recommended in the on suite guide, the NICEIC guidance for installations upto 100amps guide and note 2 from bs 7671.

Never seen rcbo instructions for Schneider rcbos I'll have to take your word on that tho it maybe the manufacturers guidance I fail to see if the resistance is greater than 100bohms has got to do with it as the max zs associated with an 30mA rcbo would be 1667 ohms!
Unless the rcbo won't work over 100 ohms in which case remind me never to use Schneider!
 

Reply to Installing 60Kva generator. in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K
Well at about 9.30 last night I stripped the door card off and found the culprit, cable snapped and end off. So I spent another hour and managed...
    • Like
    • Funny
Replies
2
Views
288

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top