Hi all,
my 1st post on the forum so please be gentle!!
I am about to install a new oven and hob in a gutted kitchen. No fuse yet, no circuit cables installed. Could someone just confirm that I am correct with my selection.
Oven 2380W
Hob 6600W
Total 9Kw, works out to draw 39Amps.
If I wish to power both from 1 circuit, 10mm T&E (enclosed in thermal wall) can carry 46Amps. So, Cable is up to the job, a 45Amp breaker will cover the load AND protect the cable.
I run the 10mm cable to a 45A fused cooker switch, run this down the wall to the cooker point and then connect both oven and hob to the point. All protected by the 45Amp MCB!!
What do you think?
All the best, Paul