Hi all,

my 1st post on the forum so please be gentle!!

I am about to install a new oven and hob in a gutted kitchen. No fuse yet, no circuit cables installed. Could someone just confirm that I am correct with my selection.

Oven 2380W
Hob 6600W

Total 9Kw, works out to draw 39Amps.

If I wish to power both from 1 circuit, 10mm T&E (enclosed in thermal wall) can carry 46Amps. So, Cable is up to the job, a 45Amp breaker will cover the load AND protect the cable.

I run the 10mm cable to a 45A fused cooker switch, run this down the wall to the cooker point and then connect both oven and hob to the point. All protected by the 45Amp MCB!!

What do you think?

All the best, Paul
 
Hiall,

final solution as follows;

6mm radial for the hob, feed side into a cooker switch, load side to an outlet, cable protected by 32Amp mcb.

13Amp fused spur for the oven, feed side connected into the kitchen ring, load side to the oven, then if the fuse blows the ring continues to operate.

One final question, cooker switches, are these rated at 13A, 20A & 45A only? If so, as this hob draws 28A max, wouldn't a 45A cooker switch rating be too high or will the MCB be sufficient enough to cover it?
 
Hi all,

many thanks for all of you help with this today.

This forum is brilliant!! I will be posting much more.

I am a qualified spark, just done 17th edition and now need to tackle inspection of my own work. Just about to sign up with NICEIC and this is one of the jobs I will get them to inspect. Any ideas on part p testers? Oh, and I don't have ÂŁ100's to spend, what about a kewtech KT61??

Paul
 
think thats down to personal preference, iv all way used fluke so when i went part p brought myself a nice shiny new fluke1653b, the way i looked at it is i only hope to by 1 of theses. so i forked out!

danny
 
6mm supply on a 32amp breaker to a cooker isolator with an integral 13amp point, mount in cupboard adjacent to the hob and plug in the cooker to the 13 amp point.


Mount in cupboard????? And then in the event of a fire you have to open the cupboard, pull out all the rubbish in the cupboard and lean intot he back of the cupboard and isolate your cooker supply (hmmmmmmmmmmmmmmmmmm, not a great idea)
 
Mount it at the front of the cupboard then, Alternatively, 6mm to a dual 35mm box put two 32amp cooker switches in, link them then put two 20mm conduit drops with 6mm T+E, to two individual single back boxes one with a 13amp single gang plate the other with a cooker outlet plate with some H07 flex to the hob, If you don't want to cut out the backs of the cupboards to access the single socket or the cooker outlet do the drops in 20mm flexi conduit to the kitchen cupboards and mount the single socket and the cooker outlet in the back.
 

Reply to Installing a new oven & hob - cable and MCB size in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
233
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
594
  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top