So my understand now is if you feed a outbuilding on a 63A and have a 50A shower on the Submain board this would also not achieve discrimination?(Just an example).
Maybe if I Install a 63A type C instead of the 50A it would then achieve discrimination?

No a type C won't help. The type of the mcb relates to its ability to handle inrush current and not its behaviour under short circuit fault conditions.

At a guess you'd need the distribution circuit to be at least 80A protected by a bs88 fuse to be able to discriminate with a 50A mcb.

in some installations it is not possible to achieve full discrimination where the company fuse just isn't big enough to be able to discriminate with. For example on a standard domestic 100A supply it's unlikely to be possible to achieve full discrimination on a larger circuit.
 
A type c will trip at between 7-10 times it's rated current between 0.1-5 seconds which is why it's max zs is lower than that of a type b and is normally associated which inductive loads
 
Last edited:
That's why I use a TYPE C due to its inductive loads, as the PSU has 100A DC breakers within it fed via the -48v DC system.
Is the calculation in the regs book for this in chapter 43
• 434.5.2
- t=k2xS2 / I2
just so I can check next time I do a circuit design it won't / Prevent happen again.

Another question i want to do training on this now so would I have to do a 2396 course?

Thanks again all.
 
That's why I use a TYPE C due to its inductive loads, as the PSU has 100A DC breakers within it fed via the -48v DC system.
Is the calculation in the regs book for this in chapter 43
• 434.5.2
- t=k2xS2 / I2
just so I can check next time I do a circuit design it won't / Prevent happen again.

Another question i want to do training on this now so would I have to do a 2396 course?

Thanks again all.
For disconnection times lower than that given in bs7671 manufacturers let through energy needs to be obtained so that the cable can withstand the fault current.
I2t <k2S2
Where k is the material operating temp and S is the CSA of the cpc.
The formula you have stated will give max time the cable will withstand the fault current before damage occurs
 

Reply to Instantaneous Trippin/Discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
926

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
275

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top