davesparks
So my understand now is if you feed a outbuilding on a 63A and have a 50A shower on the Submain board this would also not achieve discrimination?(Just an example).
Maybe if I Install a 63A type C instead of the 50A it would then achieve discrimination?
No a type C won't help. The type of the mcb relates to its ability to handle inrush current and not its behaviour under short circuit fault conditions.
At a guess you'd need the distribution circuit to be at least 80A protected by a bs88 fuse to be able to discriminate with a 50A mcb.
in some installations it is not possible to achieve full discrimination where the company fuse just isn't big enough to be able to discriminate with. For example on a standard domestic 100A supply it's unlikely to be possible to achieve full discrimination on a larger circuit.