Hi,
This may sound stupid and I may be missing something but here goes.
I have been pulled by a third party company regarding discrimination of a 50A Type C 60898 3ph MCB feeding a Submain which then has another distribution board feeding a PSU (which has 2 AC circuits and a DC consumer unit) protected by a 32A Type C 60898 3ph MCB.
The part I'm struggling with is how does this not achieve it as the 32A has 320A instantaneous tripping current and the 50A is 500A (0.1-5sec)(BS7671 Page 326).
Could someone point me in the right direction regarding the regulations and thoery please.
I'm expecting to be schooled here as I think I'm missing something simple.
Thanks in advance.