Hi everyone.
I need a little advice please. Several months ago I first fixed and second fixed a timber frame loft conversion ( open plan living area and kitchen) for a friend /client. I haven't signed it off yet as I was waiting to install I new CU for him and for him to fit the kitchen. I fitted a kitchen ring final in 2.5mm, socket radial 2.5mm, 2x 6mm hob/oven supplies, a radial, and 2 lighting circuits in 1mm. And smoke detector.1mm. At the time it was simply kingspan with cables through timbers mostly not touching the insulation I used Reference method 102 for calculations. I have however returned to connect up an electric skylight and noticed that every cavity including the 18 inch floor space has been packed with wool insulation changing the reference method to 103. As we know a ring final should not be installed when using ref meth 103 and the radial 2.5m current carrying capacity will be reduced to 13.5A, the 6mm cables to 23.5A. The walls have been plastered and the tongue and grove flooring down and glued. Does anyone have any suggestions on what I can do to remedy this situation? Many thanks in advance.
Si
 
I was under the impression that the regs required 20amps of ccc for the RFC reg to apply. I'm sure it would be fine in practise.
If it's allowed then your way is obviously simpler and better!
The only regulation that I know of specific to the RFC is 433.1.204 which covers the case of the OCPD being above the cable rating, but due to the ring structure with fused sockets along it, that is acceptable.

However, I interpreted that as saying you can use an OCPD of 1.5 times the CCC for such a RFC, not that you must use 30A fuse/32A MCB and not anything less. After all, it shows examples of the same BS1363 accessories on a 20A radial in the appendix.

Now one of the main arguments for the RFC is the greater coverage and application of diversity that comes from having 32A backing a number of sockets, versus the 20A radial (or 16A radial more common in the EU), but I never though it was obligatory.

Without wanting to kick off yet another "RFC versus Radial" argument I would still stick with the RFC as I like both the ability to check end-end via r1,r2,rN readings, and the redundancy in the CPC against a single open (which would not be spotted, unlike an open live on a radial). And here I would feel the 20A versus two radials at 16A (which is actually above 2.5mm CCC under method 103!) gives better diversity of socket use.

Maybe the "20A RFC" should be the topic of another thread!
 
Lots of people seem to think a 20A RFC is ok. As suggested I'm creating a new thread for that.
And here I would feel the 20A versus two radials at 16A (which is actually above 2.5mm CCC under method 103!) gives better diversity of socket use.
I agree that if permitted a 20A RFC is much better. I should also clarify that I don't actually like my idea, I was just trying to think of wacky approaches! Whether a good idea or not, I believe you could be in compliance with letter of regs by having a 16A breaker, method 103, and applying the downstream overload protection exemption by either having the first length within 3m or relying on RCD for fault protection. (yuck, yuck, and thrice yuck...)
Then 433.2.2 is met. It is the last think I'd want to do, and future inspectors would have a field day, but occasionally circumstances conspire and the last resort methods come out to play.
Much better for the OP to get the installation sorted out as originally intended of course!
 

Reply to Insulation added after second fixing! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top